Ha. Touché. I was meaning there was no criteria for it. Yes, it is called out 
as outside the scope. 

And I would run fast from 60’ tall rack storage of boats. 

Travis Mack, CFPS, CWBSP, RME-G, SET
480-505-9271
MFP Design, LLC
"Follow" us on Facebook: 
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

> On Feb 21, 2019, at 11:15 AM, Roland Huggins <[email protected]> 
> wrote:
> 
> Travis.  Allow me to correct your statement.  It is in NFPA 13.  Look at 
> Table A.5.6.  Although the title of this Table is weak (that being Examples 
> of Commodities Not Addressed by Classifications in Section 5.6), it should 
> say OUTSIDE THE SCOPE OF NFPA 13.
> 
> Hey I know the end result of both statements is the same - lol.  IT does make 
> a difference, though, in the discussion with the owner.
> 
> Roland 
> 
> 
> Roland Huggins, PE - Senior VP Engineering
> American Fire Sprinkler Assn.    
> Dallas, TX
> http://www.firesprinkler.org
> 
> Fire Sprinklers Saves Lives
> 
> 
> 
> 
>> On Feb 21, 2019, at 9:23 AM, Travis Mack, SET, CFPS, CWBSP, RME-G 
>> <[email protected]> wrote:
>> 
>> Nothing in NFPA standards for it.  Check with the insurance company for the 
>> project.  They may have guidance.
>>  
>> <image002.jpg>
>> Travis Mack, CFPS, CWBSP, RME-G, SET
>> MFP Design, LLC
>> 3356 E Vallejo Ct
>> Gilbert, AZ 85298
>> 480-505-9271
>> fax: 866-430-6107
>> [email protected]
>>  
>> Send large files to us via: https://www.hightail.com/u/MFPDesign
>> LinkedIn: https://www.linkedin.com/in/travismack
>>  
>> “The bitterness of poor quality remains long after the sweetness of low 
>> price is forgotten.”
>>  
>>  
>> From: Sprinklerforum <[email protected]> On 
>> Behalf Of James Crawford
>> Sent: Thursday, February 21, 2019 10:21 AM
>> To: [email protected]
>> Subject: Boat Storage
>>  
>> I have been asked to look at a new building for boat storage but cannot seem 
>> to find any guidance, has anyone done a boat storage building that can point 
>> me in the right direction.
>>  
>>  
>> Thank you
>>  
>>  
>> James Crawford
>> Phaser Fire Protection Ltd.
>> Phone  604-888-0318
>> Fax 604-888-4732
>> Cel 604-790-0938
>> Email  [email protected]
>> Web www.phaserfire.ca
>>  
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________