Steve,

 

 

It is an existing building and the Engineer wants to remove the existing
fire pump because he says the standpipes do not require it. I am not
designing anything on this one..

 

 

Greg McGahan

Genesis Fire Services, LLC

o-850-637-8535

 

From: Sprinklerforum <[email protected]> On
Behalf Of Steve Leyton
Sent: Thursday, March 7, 2019 7:18 PM
To: [email protected]
Subject: RE: GSA P100 Standpipes

 

Who is enforcing/interpreting the terms of your contract?  Assuming  you are
conscribed to design and install per the referenced standards, then this
creates a conflict in the terms and conditions of your contract that should
be clarified by RFI.   As great as the pool of knowledge about all things
water-based may be in the Forum, this is a contractual issue, not a
code-based one.

 

If the responding fire department can furnish adequate flow and pressure
(and that's a performance standard they and only they can speak to) and a
high maintenance link in the chain like a fire pump can be omitted, is that
a bad thing?   There are two aspects to a water supply that are critical:
adequacy and reliability.    The reliability of a manual standpipe system
goes to the source of water from which the FD takes suction.   If the
building has pump, would it be arranged as a booster and take suction from
that same source?  If so, then you face the same metrics for reliability
either way.   But if the building would otherwise have a pump that takes
suction from a tank that's sized for both demand and duration, then
reliability is enhanced and you have to weigh cost + maintenance +
reliability to come up with the cost/benefit scenario, but you can argue
that it's a more reliable configuration, assuming that both pump and tank
are meticulously maintained.     

 

So I don't have an answer because  you didn't really pose a question, but if
I was in your shoes and was being directed to undertake a design that didn't
conform to the code(s) and/or standard(s) that are referenced in my
contract, I'd RFI whoever has jurisdiction over my contract and ask them
(presumably the owner or their agent) for direction on how to proceed.

 

And please note well that EVERYTHING in this post is my personal opinion
only.   

 

 

Steve Leyton

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of [email protected]
<mailto:[email protected]> 
Sent: Thursday, March 07, 2019 5:05 PM
To: [email protected]
<mailto:[email protected]> 
Subject: GSA P100 Standpipes

 

For those of you design professional that have been tasked with designing a
standpipe for a GSA building, the Engineer for the govt is saying things
that appear to be true but hard to accept.

 

It appears that there is not a requirement for an AUTOMATIC standpipe in a
GSA building...just the statement that "The building's fire pump must be
sized for 

the sprinkler system requirements only if the 

local responding fire department can provide 

the necessary flow and pressure for manual 

firefighting operations (i.e., standpipes), 

through fire department connections."

 

Therefore, regardless of height or floors, a manual standpipe can be used if
the Fire Dept can provide enough water..no auto standpipe?

 

Thanks in advance, 

 

 

Greg McGahan