This is my first forum comment/assistance request.  AHJ allowed system NFPA 13R 2013.  We have a beach hotel (two story) with long narrow guest rooms only 12' wide.  In several of these rooms are built in loft sleeping areas (3) high from floor to ceiling.  The largest is 35 sq.ft.  Dimension: 5'wide x 6'-9" long x 3'-6" high.   Each sleeping area is large enough for one mattress.  All frame construction (open face).  No shelves, or drawers.  Just crawl in and sleep.  A small wood ladder in front for the top two bunks. Outside the three bunks runs  an open walkway 5'-3" wide, 12' ceiling.  Our design: A single line of sidewalls are facing the bunks using Viking  VK486 12x12 sidewall coverage.  Our question, due to the confined condition of this built-in sleeping area, is this sufficient coverage?  Thanks

--