This is my first forum comment/assistance request. AHJ allowed system
NFPA 13R 2013. We have a beach hotel (two story) with long narrow guest
rooms only 12' wide. In several of these rooms are built in loft
sleeping areas (3) high from floor to ceiling. The largest is 35
sq.ft. Dimension: 5'wide x 6'-9" long x 3'-6" high. Each sleeping
area is large enough for one mattress. All frame construction (open
face). No shelves, or drawers. Just crawl in and sleep. A small wood
ladder in front for the top two bunks. Outside the three bunks runs an
open walkway 5'-3" wide, 12' ceiling. Our design: A single line of
sidewalls are facing the bunks using Viking VK486 12x12 sidewall
coverage. Our question, due to the confined condition of this built-in
sleeping area, is this sufficient coverage? Thanks
--