I see the “cartooned” in the storage definitions but it looks like: A. it
has changed,  B. the double corrugation requirement has been removed, or C.
the definition isn’t in Chapter 3.





Thank You



*Mark E. Eckard SET*

*Fire Protection Services, LLC*

2126 US Hwy. 41 North

Perry, GA 31069

Office: 478-987-7319 (Perry) or (770) 702-0965 (Metro Atlanta)

Mobile: 478-244-6653

SYL-216



*From:* Sprinklerforum <[email protected]> *On
Behalf Of *Travis Mack, SET, CFPS, CWBSP, RME-G
*Sent:* Thursday, March 14, 2019 2:26 PM
*To:* [email protected]
*Subject:* RE: Cartoned Group A Plastics



*When needing definitions, Chap 3 of the 2016 is where you want  to start.*



*3.9.1.1 gives your definition of Cartoned.*



[image: MFP_logo_F] <http://www.mfpdesign.com/>

Travis Mack, CFPS, CWBSP, RME-G, SET

MFP Design, LLC

3356 E Vallejo Ct

Gilbert, AZ 85298

480-505-9271

fax: 866-430-6107

[email protected]



Send large files to us via: https://www.hightail.com/u/MFPDesign
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>

LinkedIn: https://www.linkedin.com/in/travismack
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>



*“**The bitterness of poor quality remains long after the sweetness of low
price is forgotten.”*





*From:* Sprinklerforum <[email protected]> *On
Behalf Of *Mark Eckard
*Sent:* Thursday, March 14, 2019 11:21 AM
*To:* [email protected]
*Subject:* Cartoned Group A Plastics



I seem to remember the definition of Cartoned when it comes to storage of
Plastics saying the “carton was constructed of double layer corrugated card
board.  I am having trouble locating this info. Isn’t this correct? Where
will I find this in the 2016 NFPA-13?



Thank You



*Mark E. Eckard SET*

*Fire Protection Services, LLC*

2126 US Hwy. 41 North

Perry, GA 31069

Office: 478-987-7319 (Perry) or (770) 702-0965 (Metro Atlanta)

Mobile: 478-244-6653

SYL-216
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to