A break tank can be partially described as a water supply component that isn't sized for the full demand and duration of a system. The issue I see is that you have to factor the recovery time into your calculation of the actual duration and that requires non-listed equipment. On the other hand, 13R requires a pump supplying the sprinkler system to be listed but NOT other aspects of the water supply such as the well heads. My guess would be yes, it's okay but I'd check with the AHJ first.
Steve Leyton -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of [email protected] Sent: Wednesday, April 03, 2019 9:26 AM To: [email protected] Subject: Private Well Pump Supplying a Break Tank Working on a new 13R system for an existing small group home. No municipal water supply, but they have two domestic wells that alternate weekly use with 60GPM pumps. Since we can't use these directly for our supply, I wanted to install a break tank (NFPA 20- 4.31) and small fire pump. Can I use the domestic wells to supply the break tank even though the well pumps are not listed for fire protection? Thanks, --- Mike Kramer FS/FA Designer [email protected] _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org