A break tank can be partially described as a water supply component that isn't 
sized for the full demand and duration of a system.   The issue I see is that 
you have to factor the recovery time into your calculation of the actual 
duration and that requires non-listed equipment.  On the other hand, 13R 
requires a pump supplying the sprinkler system to be listed but NOT other 
aspects of the water supply such as the well heads.    My guess would be yes, 
it's okay but I'd check with the AHJ first.

Steve Leyton

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Wednesday, April 03, 2019 9:26 AM
To: [email protected]
Subject: Private Well Pump Supplying a Break Tank

Working on a new 13R system for an existing small group home. No municipal 
water supply, but they have two domestic wells that alternate weekly use with 
60GPM pumps.

Since we can't use these directly for our supply, I wanted to install a break 
tank (NFPA 20- 4.31) and small fire pump. Can I use the domestic wells to 
supply the break tank even though the well pumps are not listed for fire 
protection?


Thanks,

---
Mike Kramer
FS/FA Designer