I probably need to ask the question differently.

 

What's the maximum protection area (80 sf, 100 sf, 120 sf, 196 sf, ????) and
what's the maximum spacing (10', 12', 14', ????) for standard sidewall
sprinklers installed beneath overhead doors in an extra hazard or storage
occupancy?  Section 8.7.3.1.7 isn't applicable since is specifically
addresses ordinary hazards.  Table 8.7.2.2.1 isn't applicable since it
doesn't include extra hazard nor storage.

 

Ed K

Bamford Fire

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Nick Maneen
Sent: Thursday, April 25, 2019 3:41 PM
To: [email protected]
Subject: RE: OH doors in storage areas

 

NFPA 13, 2013 edition 8.12.5.3.4 

 

Obstructions under ESFR

 


Nick Maneen, SET 

c 704.791.7789

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Ed Kramer
Sent: Thursday, April 25, 2019 4:33 PM
To: [email protected]
<mailto:[email protected]> 
Subject: OH doors in storage areas

 

I'm probably overlooking this, but where does NFPA 13 give guidance for
installing sidewall sprinklers below overhead doors in a storage warehouse?
Section 

8.4.2 (2016 edition) says I can use them beneath OH doors (no restriction on
the occupancy).  Section 8.7.3.1.7 tells me protection area and maximum
spacing in an ordinary hazard occupancy can be per light hazard
requirements.  But where do I find criteria for extra hazard and/or storage
occupancies?

 

Ed K

Bamford Fire