>From what you describe and depending on how the IBC is modified in your
area, typically the upper levels wouldn't require sprinklers.  However, I am
with you that because the lower 2 levels do require sprinklers, the entire
building requires sprinklers.  There may be a local P.E. that would disagree
and say otherwise, but I would have that in writing and blessed by the local
AHJ.

 


Nick Maneen, SET 

c 704.791.7789

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Matt Grise
Sent: Thursday, May 02, 2019 4:44 PM
To: [email protected]
Subject: partially enclosed parking

 

I am looking at a 5-level parking garage that will have 2 levels below
grade. The 2 below grade levels will be enclosed - so they will need
sprinklers, but the top 3 levels will be open. I can't recall - do the open
levels need sprinklers? I know NFPA does not normally allow a partially
protected building, but for some reason I was feeling like it might be ok to
omit sprinklers from the above grade levels.

 

Thanks!

 

Matt 

 