>> Height x .434 = Starting psi at top.
>>
>> Less friction loss at flow (pick a flow)
>>
>> Your flow test complete with a K factor!
>>
>>
>>
>>
>>
>>
>> On 5/15/2019 11:27 AM, Mike Stossel wrote:
>>
>> I have an existing building with a sprinkler system that is supplied
>by a
>> gravity tank located on the roof. They are modifying the first floor
>of
>> the building that will require hydraulic calculations. Is it
>possible to
>> mathematically create a waterflow test accurately, or do you need to
>> actually perform a water flow test at the 1st floor level?
>>
>>
>>
>> Mike Stossel *SET*
>>
>> [image: 400dpiLogoCropped]
>>
>> 36 Barren Road
>>
>> East Stroudsburg, PA 18302
>>
>> Office: 973-670-2627
>>
>> [email protected]
>>
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing
>[email protected]http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
>>
>>
>> --
>>
>> 11351 Pearl Road / Suite 101
>> Strongsville, Ohio 44136
>> Phone 440 238-4800 Fax 440 238-4876 Cell 440 724-7601
>>
>>
>> * Vince Sabolik *
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>>
>http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
>
>
>------------------------------------------------------------------------
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
Vince Sabolik
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org