Tim,

I'm not sure I understand the concern.

NFPA 24 establishes that the hydrant shall be _*at least 40'*_ from the building.  If you look elsewhere in -24 there is no paragraph which notes that a hydrant could not be further away.

It seems to me that the first inquiry should be with the local fire department to ask them the maximum distance the hydrant should be located away from the building, and providing them with information on how the building is to be used.  This is mandated in §7.2.1, which says "/Hydrants shall be provided and spaced in accordance with the requirements of the AHJ/."

As I am a member of the NFPA 24 committee, please see the disclaimer below.

sincerely,
*Ken Wagoner, SET
*Parsley Consulting***
*350 West 9th Avenue, Suite 206
*Escondido, California 92025
*****Phone 760-745-6181*
Visit the website <http://www.parsleyconsulting.com/>

IMPORTANT NOTICE: This correspondence is not a Formal Interpretation issued pursuant to NFPA Regulations. Any opinion expressed is the personal opinion of the author and does not necessarily represent the official position of the NFPA or its Technical Committees. In addition, this correspondence is neither intended, nor should it be relied upon, to provide professional consultation or services

It should be noted that the above is my opinion as a member of the NFPA Installation of Private Fire Service Mains and their Appurtenances Committee in accordance with the NFPA Regulations Governing Committee Projects and should therefore not be considered, nor relied upon, as the official position of the NFPA or its Committees



***
On 05/20/2019 11:33 AM, Easter, Tim (Contractor) wrote:

NFPA 24

        

7.2.3

        

Hydrants shall be located not less than 40ft from the buildings to be protected.

        

This seems awfully close if you have an explosive building. What is usual distance for a fire hydrant from an explosive building? The fire brigade does not fight fires here.

Best,

Timothy M. Easter

Fire Protection Engineer


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to