Check out the Bermad FP 436. It is a “pressure sustaining valve.” I’ve seen water purveyors require these so that you don’t draw the suction line below 20 psi. It is installed in the pump discharge. It also acts as your pump discharge check valve.
<http://www.mfpdesign.com/> Travis Mack, CFPS, CWBSP, RME-G, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:[email protected]> [email protected] www.mfpdesign.com Send large files to us via: <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0> https://www.hightail.com/u/MFPDesign LinkedIn: <https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0> https://www.linkedin.com/in/travismack “The bitterness of poor quality remains long after the sweetness of low price is forgotten.” From: Sprinklerforum <[email protected]> On Behalf Of Mark.Phelps Sent: Tuesday, June 18, 2019 4:26 PM To: [email protected] Subject: RE: [EXTERNAL] Re: Suction Control Valve The 2019 version of NFPA 20 goes on to say : 4.16.5.4 No control valve other than a listed OS&Y valve and the devices as permitted in <https://codesonline.nfpa.org/code/40e1327d-3fd3-4a71-860f-4ec92a4bec89/e909aaad-4058-4ae1-9c1b-0a58441efe7a/np_58253fca-f642-11e7-914a-0547f3f12f9d.html#ID000200000544> 4.29.3 shall be installed in the suction pipe within 50 ft (15.3 m) of the pump suction flange. 4.29.3 describes how to install a backflow preventer a minimum of 50 feet from the suction flange of the fire pump. I don’t find anywhere in NFPA 20 where it describes or allows a “Throttle Control Valve. Mark at Aero 602 820-7894 From: Sprinklerforum [mailto:[email protected]] On Behalf Of Timothy Goins Sent: Tuesday, June 18, 2019 3:28 PM To: [email protected] <mailto:[email protected]> Subject: Re: [EXTERNAL] Re: Suction Control Valve Please re-read my copied text from the NFPA 20, it says shall be installed on the suction line. Not should, but shall. And I will give them one heart, and I will put a new spirit within you; and I will take the stony heart out of their flesh, and will give them an heart of flesh Eze 11:19 On Jun 18, 2019, at 4:23 PM, Prahl, Craig/GVL <[email protected] <mailto:[email protected]> > wrote: On marginal municipal water supplies where there is the chance that the fire pump could draw flows greater than what could be provided, the water purveyor will often request a suction control valve. Basically, this throttles the flow from the pump and keeps the municipal system pressure from going negative. Craig Prahl | Jacobs | Group Lead – Fire Protection | 864.676.5252 | <mailto:[email protected]> [email protected] | <https://urldefense.proofpoint.com/v2/url?u=http-3A__www.jacobs.com_&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=dLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg&m=DfTAYwUJpJ5qWdFrEReH1LUJi7vmhhsyNN16NPQ7H4w&s=HvVurPrXKAWSL3gbUp-tLO7vWCSKDJaxF9EKKQ1WV5Y&e=> www.jacobs.com 1041 East Butler Road Greenville, South Carolina 29606 From: Sprinklerforum <[email protected] <mailto:[email protected]> > On Behalf Of Vince Sabolik Sent: Tuesday, June 18, 2019 5:09 PM To: [email protected] <mailto:[email protected]> ; Brian Harris <[email protected] <mailto:[email protected]> > Subject: [EXTERNAL] Re: Suction Control Valve Required by the water purveyor? On 6/18/2019 4:40 PM, Brian Harris wrote: I just got a quote for a pump on a project and they’ve (pump supplier) have included one. Most of the jobs I’ve done don’t have one… Brian Harris, CET BVS Systems Inc. bvssytemsinc.com <https://urldefense.proofpoint.com/v2/url?u=http-3A__bvssystemsinc.com_&d=DwMD-g&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=_w721WvezJkWUVteY4FMhecHAoDqOn85ooHi6vIkMag&m=h5fUnvhF7LPXqbICgBFCwQUV0IUa_zKmRvXHt6-VJjU&s=-OVMKaguEsZCJuQtVliMr7OVDwwdGAdA55Rk1B-MsfI&e=> From: Sprinklerforum <mailto:[email protected]> <[email protected]> On Behalf Of Travis Mack, SET, CFPS, CWBSP, RME-G Sent: Tuesday, June 18, 2019 4:39 PM To: [email protected] <mailto:[email protected]> Subject: RE: Suction Control Valve Every case I’ve had one is because the water purveyor required it. <https://urldefense.proofpoint.com/v2/url?u=http-3A__www.mfpdesign.com_&d=DwMD-g&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=_w721WvezJkWUVteY4FMhecHAoDqOn85ooHi6vIkMag&m=h5fUnvhF7LPXqbICgBFCwQUV0IUa_zKmRvXHt6-VJjU&s=tGaOOsh54Shm26msSYTu24ovesV1Q8_0Nw4rzyhHwEE&e=> <image001.jpg> Travis Mack, CFPS, CWBSP, RME-G, SET MFP Design, LLC 3356 E Vallejo Ct Gilbert, AZ 85298 480-505-9271 fax: 866-430-6107 <mailto:[email protected]> [email protected] www.mfpdesign.com <https://urldefense.proofpoint.com/v2/url?u=http-3A__www.mfpdesign.com&d=DwMD-g&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=_w721WvezJkWUVteY4FMhecHAoDqOn85ooHi6vIkMag&m=h5fUnvhF7LPXqbICgBFCwQUV0IUa_zKmRvXHt6-VJjU&s=yI741w_t2pSo-IhT5f0s1hOpCJmyS5HcQ4HjxjNMdWQ&e=> Send large files to us via: https://www.hightail.com/u/MFPDesign LinkedIn: https://www.linkedin.com/in/travismack “The bitterness of poor quality remains long after the sweetness of low price is forgotten.” From: Sprinklerforum <[email protected] <mailto:[email protected]> > On Behalf Of Brian Harris Sent: Tuesday, June 18, 2019 1:39 PM To: [email protected] <mailto:[email protected]> Subject: Suction Control Valve Who/What determines when a Suction Control Valve is needed? Brian Harris, CET BVS Systems Inc. Design Manager bvssystemsinc.com <https://urldefense.proofpoint.com/v2/url?u=http-3A__bvssystemsinc.com_&d=DwMD-g&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=_w721WvezJkWUVteY4FMhecHAoDqOn85ooHi6vIkMag&m=h5fUnvhF7LPXqbICgBFCwQUV0IUa_zKmRvXHt6-VJjU&s=-OVMKaguEsZCJuQtVliMr7OVDwwdGAdA55Rk1B-MsfI&e=> Phone: 704.896.9989 Fax: 704.896.1935 _______________________________________________ Sprinklerforum mailing list [email protected] <mailto:[email protected]> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org <https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwMD-g&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=_w721WvezJkWUVteY4FMhecHAoDqOn85ooHi6vIkMag&m=h5fUnvhF7LPXqbICgBFCwQUV0IUa_zKmRvXHt6-VJjU&s=Ry4A47iB8Db4ZBrk7GLE7LdZ4S33Wt-ZjWSOtI11mRA&e=> -- <image002.png> Vince Sabolik West Tech Fire Protection, Inc. 11351 Pearl Road / Strongsville, Ohio 44136 Phone 440 238-4800 Fax 440 238-4876 Cell 440 724-7601 _____ NOTICE - This communication may contain confidential and privileged information that is for the sole use of the intended recipient. Any viewing, copying or distribution of, or reliance on this message by unintended recipients is strictly prohibited. If you have received this message in error, please notify us immediately by replying to the message and deleting it from your computer. _______________________________________________ Sprinklerforum mailing list [email protected] <mailto:[email protected]> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org <https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=dLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg&m=DfTAYwUJpJ5qWdFrEReH1LUJi7vmhhsyNN16NPQ7H4w&s=3C3Ilb_HQIn0ZS9Zwv2YK4F7Axv1h4fmjWTC9lAk6tY&e=>
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org