It doesn't.  NFPA 13 talks about obstructions over 48" in width but there are 
also other factors that come into play when dealing with obstructions.

Chapter 8 deals with horizontal and vertical obstruction rules and helps you 
determine when and where additional sprinklers are required.  There are 
numerous conditions where obstruction rules can come into play.

The 36" diameter thing is from FM Global.

Craig Prahl | Jacobs | Group Lead - Fire Protection | 864.676.5252 | 
[email protected]<mailto:[email protected]> | 
www.jacobs.com<http://www.jacobs.com/>
1041 East Butler Road   Greenville, South Carolina  29606

From: Sprinklerforum <[email protected]> On Behalf 
Of Easter, Tim (Contractor)
Sent: Wednesday, June 19, 2019 9:37 AM
To: [email protected]
Subject: [EXTERNAL] obstruction

Hi,
Where does it say in NFPA 13 or another code, that you must provide sprinklers 
under obstructions that are 3' in diameter?

Best,