Text below is specific to areas with combustible construction. So if the area 
is of non-combustible construction and doesn't contain any combustible 
material, it would appear that there is no restriction.

2019 NFPA 13, A.9.1 Where buildings or portions of buildings are of combustible 
construction or contain combustible material, standard fire
barriers should be provided to separate the areas that are sprinkler protected 
from adjoining unsprinklered areas. All openings
should be protected in accordance with applicable standards, and no sprinkler 
piping should be placed in an unsprinklered area unless the area is permitted 
to be unsprinklered by this standard.

Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | 864.676.5252 | 
[email protected]<mailto:[email protected]> | 
www.jacobs.com<http://www.jacobs.com/>
1041 East Butler Road   Greenville, South Carolina  29606

From: Sprinklerforum <[email protected]> On Behalf 
Of Travis Mack, SET, CFPS, CWBSP, RME-G
Sent: Monday, July 15, 2019 7:11 PM
To: [email protected]
Subject: [EXTERNAL] partial systems - running piping through unprotected areas

My memory is failing me today.  Isn't there a section that says I can't run 
piping through un-protected areas?  We have a building that has a partially 
protected basement.  Basically, we have to bulk across the basement to protect 
3 areas.  Can some one help me find the section of 13 that says this is 
acceptable or not?

[MFP_logo_F]<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.mfpdesign.com_&d=DwMFAg&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=_w721WvezJkWUVteY4FMhecHAoDqOn85ooHi6vIkMag&m=9pUQ5gNFlZTj08HuVuXX5QtE57m20I8wgbvhPpKQoT0&s=T0juGEMN118qEHFUT_kDsWOjCuK1Aj48ve8LXK3nQOc&e=>
Travis Mack, CFPS, CWBSP, RME-G, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
[email protected]<mailto:[email protected]>
www.mfpdesign.com<http://www.mfpdesign.com>

Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://urldefense.proofpoint.com/v2/url?u=https-3A__na01.safelinks.protection.outlook.com_-3Furl-3Dhttps-253A-252F-252Fwww.hightail.com-252Fu-252FMFPDesign-26data-3D02-257C01-257C-257C1121d49f9e6b4cf248f108d4df580e77-257C14e5497c16da42e69ffa77d19bafe511-257C0-257C0-257C636379016677342180-26sdata-3DeGdMZGu2wXhUupGwgGTrqF3b54OP5-252BAZvlHhABSexWY-253D-26reserved-3D0&d=DwMFAg&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=_w721WvezJkWUVteY4FMhecHAoDqOn85ooHi6vIkMag&m=9pUQ5gNFlZTj08HuVuXX5QtE57m20I8wgbvhPpKQoT0&s=-rh2NzEV2PMUCrcx2lzeM4yggasv5yFx7XL9aPNOkkE&e=>
LinkedIn: 
https://www.linkedin.com/in/travismack<https://urldefense.proofpoint.com/v2/url?u=https-3A__na01.safelinks.protection.outlook.com_-3Furl-3Dhttps-253A-252F-252Fwww.linkedin.com-252Fin-252Ftravismack-26data-3D02-257C01-257C-257C1121d49f9e6b4cf248f108d4df580e77-257C14e5497c16da42e69ffa77d19bafe511-257C0-257C0-257C636379016677342180-26sdata-3DtT5E7LsZjSmyreKi4gDCa70EWN-252BZodi-252FhbeCbHNRijI-253D-26reserved-3D0&d=DwMFAg&c=OgZOSER8c1RLeytEexU279Q2qk0jVwkrOdYe5iSi-kk&r=_w721WvezJkWUVteY4FMhecHAoDqOn85ooHi6vIkMag&m=9pUQ5gNFlZTj08HuVuXX5QtE57m20I8wgbvhPpKQoT0&s=8lRbUXL0hZnfPA0iMIaiFiPYaxXC1W98fM4N8-hAv2M&e=>

"The bitterness of poor quality remains long after the sweetness of low price 
is forgotten."



________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to