Typically we would not choose a diesel pump if our pump room were in a basement or any room where we could not get the exhaust out of the room with the shortest possible length of pipe.
Discharging exhaust into a parking basement would need to be approved by a building code official since this could pose a hazard to people who might be in the parking area if the pump were running. You also need to speak to the pump manufacturer about the length of the exhaust because excess length affects pump performance. The ventilation system may not be suitable for moving diesel exhaust. Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 864.676.5252 | [email protected]<mailto:[email protected]> | www.jacobs.com<http://www.jacobs.com/> 1041 East Butler Road Greenville, South Carolina 29606 From: Sprinklerforum <[email protected]> On Behalf Of Phong - Indochine Engineering Sent: Wednesday, July 31, 2019 4:21 AM To: [email protected] Subject: [EXTERNAL] Engine Exhaust of a Diesel fire pump Dear All, I have this fire pump installed inside a pump room in a basement of a high rise tower. The space of basement outside the pump room is for parking. Read 11.5 of NFPA 20:2019 and I design to select the exhaust discharge location just outside the pump room, and inside the parking basement. The basement have its dedicated auto operated ventilation system. Is my design not wrong to NFPA? Thanks. Regards, Le Vu Phong Mobile: +84 (0) 902 363 525 ________________________________ NOTICE - This communication may contain confidential and privileged information that is for the sole use of the intended recipient. Any viewing, copying or distribution of, or reliance on this message by unintended recipients is strictly prohibited. If you have received this message in error, please notify us immediately by replying to the message and deleting it from your computer.
_______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org