The temperature rating is a whole separate issue.  Due to the structural
layout of this existing building, the ESFR's are  not on a 10' x 10'
spacing. So literally impossible to get heaters 7' away.  Still working on
that one.  May have to go to another source of heat.

 

Back to the 'obstruction at or near ceiling'.  Without 13 giving any other
clarification, I interpret 8.12.5.2 to apply to any isolated obstruction
that is entirely below the elevation of the sprinkler - even if it's only
1/2".  I believe 8.12.5.1 is titled "Obstructions at or near ceilings"
because it applies to objects who's tops  are located in the space between
the ceiling and the sprinkler deflector.  Any objects that are located
entirely below the deflector kicks you to 8.12.5.2 or 8.12.5.3.  I'll admit,
I don't work with ESFR's every day, but having read those sections multiple
times, that's all I come up with.  

 

Ed K

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Kyle.Montgomery via Sprinklerforum
Sent: Tuesday, August 20, 2019 9:48 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Kyle.Montgomery <kmontgom...@aerofire.com>; Ed Kramer
<e...@bamfordfire.com>
Subject: RE: [EXTERNAL] ESFR's and unit heaters

 

Also, how are you complying with the temperature rating when you are that
close to a unit heater? Are they making any high temperature ESFRs yet?

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Kyle.Montgomery via Sprinklerforum
Sent: Tuesday, August 20, 2019 7:40 AM
To: sprinklerforum@lists.firesprinkler.org
<mailto:sprinklerforum@lists.firesprinkler.org> 
Cc: Kyle.Montgomery <kmontgom...@aerofire.com
<mailto:kmontgom...@aerofire.com> >; Ed Kramer <e...@bamfordfire.com
<mailto:e...@bamfordfire.com> >
Subject: RE: [EXTERNAL] ESFR's and unit heaters

 

I'm looking at the code again, and you may be right. But I always thought
that an obstruction that close to the sprinkler (could you quantify "just
below the ESFR deflectors") would have to meet the rules for "Obstruction at
or Near Ceiling", 8.12.5.1.

 

Are we saying that 8.12.5.1 only applies if the obstruction extends above
the deflector? I thought that anything in that 0"-31" below the deflector
range (shown in Table 8.12.5.1.1) was considered "at or near the ceiling".

 

Kyle Montgomery

 

Aero Automatic Sprinkler Co.

21605 N. Central Ave.

Phoenix, AZ 85024

Direct: 623.580.7820

Cell: 602.763.4736

 <mailto:kmontgom...@aerofire.com> kmontgom...@aerofire.com

 

 

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Ed Kramer via Sprinklerforum
Sent: Tuesday, August 20, 2019 6:23 AM
To: sprinklerforum@lists.firesprinkler.org
<mailto:sprinklerforum@lists.firesprinkler.org> 
Cc: Ed Kramer <e...@bamfordfire.com <mailto:e...@bamfordfire.com> >
Subject: [EXTERNAL] ESFR's and unit heaters

 

I'm looking for a bit of a reality check this morning.   Got an ESFR
sprinkler system and unit heaters.  In plan view, the heaters are 21" by
40".  Top of the heaters will be just below the ESFR deflectors, and they
will be located at least 1' horizontally from the ESFR sprinklers.  It
appears that NFPA 13 (2013) section 8.12.5.2 applies.

 

Subsection (2) reads: "Additional sprinklers shall not be required where the
obstruction is 2 ft or less in width and the sprinkler is located
horizontally 1 ft or greater from the nearest edge of the obstruction."

 

Since the heater is 2' or less in its smaller dimension (width), does it
matter that the other dimension (length) is greater than 2'?  I say the
length is not relevant (unless its long enough to obstruct more than 1
sprinkler, then section 8.12.5.3 applies), and subsection (2) allows me to
not install a sprinkler below these heaters.

 

How do the rest of you interpret this?

 

Thanks

Ed Kramer