Just FYI about this - Notice that in the 2017 edition the highlighted text [all 
portions of cold storage areas] was removed in the annex material as an example 
of a harsh environment for sprinklers.

2014 NFPA 25:
5.3.1.1.2* Where sprinklers are subjected to harsh environments, including 
corrosive atmospheres and corrosive water supplies, on a 5-year basis, either 
sprinklers shall be replaced or representative sprinkler samples shall be 
tested.
A.5.3.1.1.2 Examples of these environments are paper mills, packing houses, 
tanneries, alkali plants, organic fertilizer plants, foundries, forge shops, 
fumigation areas, pickle and vinegar works, stables, storage battery rooms, 
electroplating rooms, galvanizing rooms, steam rooms of all descriptions 
including moist vapor dry kilns, salt storage rooms, locomotive sheds or 
houses, driveways, areas exposed to outside weather, around bleaching equipment 
in flour mills, all portions of cold storage areas, and portions of any area 
where corrosive vapors prevail. Harsh water environments include water supplies 
that are chemically reactive.
5.3.1.1.3 Where historical data indicate, longer intervals between testing 
shall be permitted.


2017 NFPA 25:
5.3.1.1.2* Where sprinklers are subjected to harsh environments, including 
corrosive atmospheres and corrosive water supplies, on a 5-year basis, either 
sprinklers shall be replaced or representative sprinkler samples shall be 
tested.
A.5.3.1.1.2 Examples of these environments are paper mills, packing houses, 
tanneries, alkali plants, organic fertilizer plants, foundries, forge shops, 
fumigation areas, pickle and vinegar works, stables, storage battery rooms, 
electroplating rooms, galvanizing rooms, steam rooms of all descriptions 
including moist vapor dry kilns, salt storage rooms, locomotive sheds or 
houses, driveways, areas exposed to outside weather, around bleaching equipment 
in flour mills, and portions of any area where corrosive vapors prevail. Harsh 
water environments include water supplies that are chemically reactive.
5.3.1.1.3 Where historical data indicate, longer intervals between testing 
shall be permitted.


Respectfully,

David Blackwell

David Blackwell, P.E.
Chief Engineer
(803)896-9833

Office of State Fire Marshal
141 Monticello Trail | Columbia, SC 29203
http://statefire.llr.sc.gov/
(803)896-9800

"Our firefighting starts with plan review..."

From: Sprinklerforum <[email protected]> On Behalf 
Of Kaiser, Dan (DPS) via Sprinklerforum
Sent: Tuesday, August 20, 2019 3:31 PM
To: [email protected]
Cc: Kaiser, Dan (DPS) <[email protected]>
Subject: RE: Dry Flex Balcony Sprinklers

*** SCDLLR NOTICE ***

•  This email is from an external email address. Please use caution when 
deciding whether to open any attachments or when clicking links.
•  Personally Identifiable Information (PII) should not be included in e-mail 
text or attachments. Do not save or transmit PII unencrypted.
[cid:[email protected]]

[cid:[email protected]]

Dan Kaiser

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Mike Kramer via Sprinklerforum
Sent: Tuesday, August 20, 2019 10:16 AM
To: 
[email protected]<mailto:[email protected]>
Cc: [email protected]<mailto:[email protected]>
Subject: Dry Flex Balcony Sprinklers

Has anyone seen any information about inspecting dry flex balcony sprinklers 
after being installed? Regular dry sprinklers need to be inspected, tested, or 
replaced every 10 years. Mainly wondering if the flex dry sprinklers are any 
different because most of the time they will be impossible to remove without 
cutting drywall or siding out.


Mike Kramer
---
Sent from my Windows PC with GMX 
Mail<https://gcc01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.microsoft.com%2Fstore%2Fapps%2F9WZDNCRDRH19%3Fcid%3Dsignature_link&data=02%7C01%7Cdan.kaiser%40state.mn.us%7C81c967fb9eff478785e008d725814648%7Ceb14b04624c445198f26b89c2159828c%7C0%7C0%7C637019109468265221&sdata=eiSSIhW2FlR2hC5wh1M06xoLCmrE6fCzo4jws4l2VCs%3D&reserved=0>.