Jerry,

I've seen situation where they added thicker insulation at the ridgeline to 
account for a few inches of height. If it's a relatively small area that's over 
30 feet, that might be a cost-effective solution.

I believe that you can use the design criteria (head pressure) for the roof 
height in the area of the building that you are in. You typically have to 
extend the higher criteria 15 feet past the point where the ceiling height 
changes. In your case, you could use the 35-foot criteria and extend that 15 
feet past the breaking point where it drops under 30-feet. In your case, if the 
beam acts as a sort of draft stop, maybe you can just draw the line there 
rather than extending it. I'm not certain on the spacing, but I don't see why 
you couldn't do that. Calcs can be weird if the different criteria is part of 
the same system, but it might be easier if you are using a beam as the 
separation rather than just a point where the roof height changes.

-Kyle M

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Mike Hairfield via Sprinklerforum
Sent: Tuesday, August 20, 2019 4:52 PM
To: [email protected]
Cc: Mike Hairfield <[email protected]>
Subject: [EXTERNAL] Re: ESFR Sprinklers Spacing and Height Criteria

No and No

________________________________
From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 on behalf of Jerry Van Kolken via Sprinklerforum 
<[email protected]<mailto:[email protected]>>
Sent: Tuesday, August 20, 2019 7:51 PM
To: 
[email protected]<mailto:[email protected]>
 
<[email protected]<mailto:[email protected]>>
Cc: [email protected]<mailto:[email protected]> 
<[email protected]<mailto:[email protected]>>
Subject: ESFR Sprinklers Spacing and Height Criteria


**I know this is something I would need to get a waiver on by the AHJ.

  1.  I have a building just over 30'-0" by 4" does anyone how critical these 
4" are, if the 30'-0" criteria were used?



  1.  Also the building has Wide Flanges beams sectioning off the Roof. Could 
one use the under 30'-0" spacing criteria (12'-0") in these lower bays even if 
it is still the same room as the high roof?