23.4.4.1. Replace “Remote” with “hydraulically most demanding”. Hydraulically most demanding is not always a perfect rectangle. Use the 1.2X as the starting point and go from there. Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080 (ofc) 860-553-3553 (fax) 860-608-4559 (cell)
> > On Sep 11, 2019 at 8:15 PM, <Jerry Van Kolken via Sprinklerforum > (mailto:[email protected])> wrote: > > > > > > Over the years I’ve come across some Remote areas that don’t fit into the > nice rectangle /square shape. I was curious if some you would like to share > how you approached these? > > > > > > > > > > > > The one I’m currently looking at is a Tree system feeding into a U-shaped end > of the system area. The main runs into one part of the U while the last line > rounds a corner into the other part of the U another 20’-0”. This is a > light hazard area so would you start at the end of the line and run the (1.2X > Sq root 1500) ~46.5’ then jump to the next line. Or start with the head near > the corner where the lines would be more typical to get a more rectangle > shape remote area? > > > > > > > > Jerry Van Kolken > > > > Millennium Fire Protection Corp. > > > > 2950 San Luis Rey Rd. > > > > Oceanside, CA 92058 > > > > (760) 722-2722 FX 722-2730 > > > > > > > _______________________________________________ Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org >