Is there any code reference because I lost the argument several times.

Let's say you have an area with a cloud ceiling with interstitial. Deck is 15' 
between floors with beam construction and the ceiling cloud is 8' with a gap 
requiring interstitial.


Thanks



Sent from my cell phone. Please excuse spelling etc.



Mark Phillips
Vice President of Fire Protection, Kirlin Carolinas, LLC
t: 919-526-1584 | m: 919-610-0490
mphill...@jjkllc.com | https://kirlingroup.com
8000 Brownleigh Dr, Raleigh, NC 27617
-------- Original message --------
From: Matthew J Willis via Sprinklerforum 
<sprinklerforum@lists.firesprinkler.org>
Date: 9/20/19 7:49 PM (GMT-05:00)
To: sprinklerforum@lists.firesprinkler.org, vi...@wtfp.net
Cc: Matthew J Willis <ma...@rapidfireinc.com>, "Travis Mack, SET, CFPS, CWBSP, 
RME-G" <tm...@mfpdesign.com>
Subject: Re: COMBUSTIBLE CEILING SPACE

Caution: This email originated from outside the organization. Do not click 
links or open attachments unless you recognize the sender and know the content 
is safe.
Concur.
Works in an attic as well.


Matt

On the road..

________________________________
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> on behalf 
of Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum 
<sprinklerforum@lists.firesprinkler.org>
Sent: Friday, September 20, 2019 5:47:17 PM
To: vi...@wtfp.net <vi...@wtfp.net>; sprinklerforum@lists.firesprinkler.org 
<sprinklerforum@lists.firesprinkler.org>
Cc: Travis Mack, SET, CFPS, CWBSP, RME-G <tm...@mfpdesign.com>
Subject: RE: COMBUSTIBLE CEILING SPACE

It is my understanding you can use the ceiling with the pendent sprinklers as 
the floor level when measuring the QR reduction.

[MFP_logo_F]<http://www.mfpdesign.com/>
Travis Mack, CFPS, CWBSP, RME-G, SET
MFP Design, LLC
3356 E Vallejo Ct
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
tm...@mfpdesign.com<mailto:tm...@mfpdesign.com>
www.mfpdesign.com

Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
LinkedIn: 
https://www.linkedin.com/in/travismack<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”


From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Vince Sabolik via Sprinklerforum
Sent: Friday, September 20, 2019 4:46 PM
To: Vince Sabolik via Sprinklerforum <sprinklerforum@lists.firesprinkler.org>
Cc: Vince Sabolik <vi...@wtfp.net>
Subject: Re: COMBUSTIBLE CEILING SPACE

Thanks, guys.

I thought similar. Why do you suppose the height applies from the floor below
when the ceiling is non com?

A case of fire insurance for cast iron under water?

Thanks again, have a nice weekend!

                                                                           Vince






On 9/20/2019 7:36 PM, Vince Sabolik via Sprinklerforum wrote:
The area above the ceiling requires protection.
Is the reduced area (use of QR) applicable?
--
[cid:image002.png@01D56FD3.0FCEA080]

Vince Sabolik
West Tech Fire Protection, Inc.
11351 Pearl Road   /   Strongsville, Ohio   44136
Phone 440 238-4800    Fax  440 238-4876   Cell 440 724-7601



_______________________________________________

Sprinklerforum mailing list

Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

--
[cid:image002.png@01D56FD3.0FCEA080]

Vince Sabolik
West Tech Fire Protection, Inc.
11351 Pearl Road   /   Strongsville, Ohio   44136
Phone 440 238-4800    Fax  440 238-4876   Cell 440 724-7601
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
  • COMBUSTIBLE CEILIN... Vince Sabolik via Sprinklerforum
    • RE: COMBUSTIB... Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
    • Re: COMBUSTIB... Phillips, Mark via Sprinklerforum
    • RE: COMBUSTIB... Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
      • Re: COMBU... Matthew J Willis via Sprinklerforum
        • Re: C... Phillips, Mark via Sprinklerforum
          • R... Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
            • ... Matthew J Willis via Sprinklerforum
              • ... Ron Greenman via Sprinklerforum
                • ... Travis Mack via Sprinklerforum
                • ... Matthew J Willis via Sprinklerforum
                • ... cliff--- via Sprinklerforum

Reply via email to