My take on this issue:  For standard spray upright sprinklers, the "Three Times 
Rule" applies to this situation.  However, 8.6.5.2.1.8 states 8.6.5.2.1.3 shall 
not apply to sprinkler piping less than 3" in diameter.

I think the language was changed because the "Three Times Rule" was added.

Thanks,
John

John August Denhardt, P.E.
Strickland Fire Protection Incorporated
4011 Penn Belt Place
Forestville, Maryland 20747-4737
301.474.1136 - Office
301.343.1457 - Mobile

From: Sprinklerforum <[email protected]> On Behalf 
Of Bruce Hermanson via Sprinklerforum
Sent: Tuesday, October 8, 2019 11:58 AM
To: [email protected]
Cc: Bruce Hermanson <[email protected]>
Subject: Upright Sprinkler

Did NFPA remove the requirement where upright sprinklers attached to pipe 3" or 
larger needs to be on a sprig?
I remember seeing it in past editions but cannot find it in 2016.


Bruce Hermanson