My take on this issue: For standard spray upright sprinklers, the "Three Times Rule" applies to this situation. However, 8.6.5.2.1.8 states 8.6.5.2.1.3 shall not apply to sprinkler piping less than 3" in diameter.
I think the language was changed because the "Three Times Rule" was added. Thanks, John John August Denhardt, P.E. Strickland Fire Protection Incorporated 4011 Penn Belt Place Forestville, Maryland 20747-4737 301.474.1136 - Office 301.343.1457 - Mobile From: Sprinklerforum <[email protected]> On Behalf Of Bruce Hermanson via Sprinklerforum Sent: Tuesday, October 8, 2019 11:58 AM To: [email protected] Cc: Bruce Hermanson <[email protected]> Subject: Upright Sprinkler Did NFPA remove the requirement where upright sprinklers attached to pipe 3" or larger needs to be on a sprig? I remember seeing it in past editions but cannot find it in 2016. Bruce Hermanson President TSFP 47810 Galleon Drive Plymouth, MI 48170 (734) 454-1350