In our State of South Carolina where we have not modified the text of 2015 IFC 
903.1.1, it has two requirements, the first part that is often overlooked is 
that it must be recognized by the applicable standard, not just approved by the 
fire code official:

903.1.1 Alternative protection. Alternative automatic fire extinguishing
systems complying with Section 904 shall be
permitted instead of automatic sprinkler protection where
recognized by the applicable standard and approved by the
fire code official.

2013 NFPA 13 Section 22.14.2.3 is an example of where such a sprinkler 
trade-off is recognized by an applicable sprinkler standard:
[cid:image003.png@01D57E99.71DCF5E0]

Respectfully,

David Blackwell

David Blackwell, P.E.
Chief Engineer
(803)896-9833

Office of State Fire Marshal
141 Monticello Trail | Columbia, SC 29203
http://statefire.llr.sc.gov/
(803)896-9800

"Our firefighting starts with plan review..."

From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Nick Maneen via Sprinklerforum
Sent: Wednesday, October 9, 2019 11:49 AM
To: sprinklerforum@lists.firesprinkler.org
Cc: Nick Maneen <nman...@sentryfp.com>; 'Dane Long' <da...@bamfordfire.com>
Subject: RE: Securing Institutional Heads

*** SCDLLR NOTICE ***

*  This email is from an external email address. Please use caution when 
deciding whether to open any attachments or when clicking links.
*  Personally Identifiable Information (PII) should not be included in e-mail 
text or attachments. Do not save or transmit PII unencrypted.
It varies from state to state with the adoption of different forms of the ICC 
Fire Code.  Here in NC, 903.1.1 allows for alternate fire extinguishing systems 
when approved by the fire code official.

Nick Maneen, SET
c 704.791.7789


From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Dane Long via Sprinklerforum
Sent: Wednesday, October 09, 2019 11:39 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Cc: Dane Long
Subject: RE: Securing Institutional Heads

Does anyone know of any codes that help omit sprinklers from bank vaults?

Thanks,

[cid:image005.png@01D57E99.71DCF5E0]

[cid:image006.png@01D57E99.71DCF5E0]



Dane Long, CET
Design Technician | Bamford Fire Sprinkler Co., Inc.
P:    785.825.7710
F:    785.825.0667
A:   1383 W. North Street  Salina, KS  67401



From: Sprinklerforum 
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Larrimer, Peter A via Sprinklerforum
Sent: Wednesday, October 9, 2019 8:20 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Cc: Larrimer, Peter A <peter.a.larri...@va.gov<mailto:peter.a.larri...@va.gov>>
Subject: RE: Securing Institutional Heads

Phil,

Are you using the institutional heads in a prison facility with "thick" 
ceilings such that the details in the typical sprinkler cut sheet would work, 
or in a medical psychiatric institution such that the ceilings are "thin" 
constructed of sheet rock or similar.  We have had issues where the cut sheet 
details with the retaining flange don't work for psyche areas due to the thin 
ceiling construction.  You have to come up with other options and we haven't 
had any manufacturer really help us with details.  We've had to work that out 
on an individual basis.

Most of the time when we specify institutional sprinklers, the installation is 
not done in accordance with the manufacturers cut sheet because the cut sheet 
details are limited and don't fit the construction type of our facilities.  
Thus, most of the institutional sprinklers can be pulled away from the ceiling 
allowing someone to hang from the escutcheon.  Unless someone is really looking 
at the installation closely, they sprinklers are installed just like any other 
type.  Unfortunately, we only find out about a bad installation after an 
incident.

We have had suicides from hanging and are not really worried about the razor 
blades as suggested in another post.  If you come up with some good suggestions 
that would help prevent someone from establishing an anchor point for hanging, 
I would appreciate hearing about them.

We have considered using a "spacer" above the ceiling to use the retainer 
flange as one option.  (We considered a pvc pipe cut in half with a retaining 
flange for an existing installation in one case after an incident.)  Another 
suggestion, when the flange doesn't work, is to ensure that hangers are located 
directly above the sprinkler so that there is minimal deflection if someone 
tries to pull down the sprinkler away from the ceiling.  Pipe clamps have been 
suggested as well, but overall, we haven't come up with anything that works for 
all cases.

Look forward to hearing about some good ideas.

Thanks

Pete Larrimer
VHA

From: Sprinklerforum 
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Kerschner, Philip via Sprinklerforum
Sent: Tuesday, October 8, 2019 3:35 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Cc: Kerschner, Philip 
<pkersch...@ballinger.com<mailto:pkersch...@ballinger.com>>
Subject: [EXTERNAL] Securing Institutional Heads

Certain institutional heads come with a retaining flange for installation above 
the ceiling to prevent the heads from being pulled away from the ceiling.  For 
instance, one sprinkler manufacturer has a FAQ that includes:

The retaining flange is provided as a way of securing the branch line piping, 
in the form of a nipple or arm-over, to prevent pipe movement initiated by the 
room occupant. If the retaining flange cannot be used due to larger piping or 
over-sized wall sleeves, alternative devices approved by the installing 
contractor or design engineer may be used to secure the piping from movement.

Has anybody used 'alternate devices' to prevent tampering from inside of the 
room.  I was considering placing a hanger on each side of the riser nipple but 
curious to hear what others may have done.