This is correct and very relevant to the design of open head fixed spray 
systems. There are many other considerations relative to this type of system 
that must be considered and complied with. Many years ago this type of work was 
appropriately termed “Special Hazard” and as the term suggests, it is 
definitely Special!

Mark at Aero
602 820-7894


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Ben Young via Sprinklerforum
Sent: Friday, October 18, 2019 9:03 AM
To: 321 via Sprinklerforum <[email protected]>
Cc: Ben Young <[email protected]>; Mark.Phelps <[email protected]>
Subject: [EXTERNAL] Re: deluge sprinkler

Just to try and keep this simple as well, if all of that is protected by a one 
single deluge system then you have to calc it all because its open. That's how 
deluge systems work, right?
If you have separate deluge systems then you have to look at if its possible 
for a fire to activate more than one system with the same fire (say two levels 
with a large open communicating space, or open grate flooring? Or even just two 
tanks that are close together.

Benjamin Young


On Fri, Oct 18, 2019 at 11:12 AM Mark.Phelps via Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 wrote:
If you haven’t gotten a response on this question, I’ll offer a couple of 
questions to gather information.

1.       Are there exterior walls that enclose the individual floors?

2.       Are the floors solid with large openings, or grated with large 
openings?

3.       What type of equipment is housed on the floors.

4.       What industry do these buildings serve?
If you can provide this information, I believe you will get some responses to 
your questions.
Mark at Aero
602 820-7894
From: Sprinklerforum 
[mailto:[email protected]<mailto:[email protected]>]
 On Behalf Of Easter, Tim (Contractor) via Sprinklerforum
Sent: Friday, October 18, 2019 5:12 AM
To: 
[email protected]<mailto:[email protected]>
Cc: Easter, Tim (Contractor) 
<[email protected]<mailto:[email protected]>>
Subject: [EXTERNAL] deluge sprinkler

Which NFPA code and section describe a situation in the building with a deluge 
system, that drive the requirement to flow all floors, both buildings 
simultaneously? The floors have large openings between floors for equipment. 
There are no walls separating different sections of  a single floor.

Best,
Timothy M. Easter, P.E.
Fire Protection Engineer
BAE Systems, Inc.
T: +1 423 578 1713  |  E: 
[email protected]<mailto:[email protected]>

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=dLwiR71i_XhSFqam3ZLeaFLiQJ3cDTUB0ReB4-yDDcg&m=f-fa0jxrYwPBQ5-W2CUUOKr4Urkwwi2lVxwwX6sIULA&s=TV6r5q5vTRWWtfN0kbn_15PlgYF_8sjjkSEXwYj4Pvo&e=>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to