Owen:

  1.   Because it could trigger a meter up-size that might cost $$thousands.
  2.   Because there's no statistical substantiation for over-protecting a 
freestanding garage with dead attic space above,   If it was a dwelling unit 
above it would be a .05, so why would a "basic" garage require more?   
According to NFPA, fewer than 3% of home fires started in the garage, nearly 
all of those from hot work.
  3.  Because it's not required by the code and referenced standards.
  4.  The reason it's not required is that the intent of home fire sprinkler 
protection is life-safety and not property protection.

Now, if you're willing to subsidize the cost impact of a higher density, I'm 
sure both the contractor and owner of the subject property would love to hear 
from you.   But why stop there - if you look at it as a detached parking 
structure, the correct density is .15.

Steve L.

________________________________
From: Sprinklerforum <[email protected]> on behalf 
of firstin--- via Sprinklerforum <[email protected]>
Sent: Thursday, December 5, 2019 9:02 PM
To: [email protected] 
<[email protected]>
Cc: [email protected] <[email protected]>
Subject: Re: Detached Garage

The thinking being why not spend a few extra bucks and protect the structure 
and contents with greater density. Makes no sense to buy time for escape with 
.05.

Sent from my iPhone

On Dec 5, 2019, at 8:14 PM, Steve Leyton via Sprinklerforum 
<[email protected]> wrote:


This issue was not clearly defined in the current 2016 California code set but 
if you look to the 2019, there is new material that very clearly states that 
this would be per 13D.  Utility occupancies that are accessory to an SFD are to 
be protected by that standard.



Steve Leyton

(Sent from my phone; please excuse typos and voice text corruptions.)




-------- Original message --------
From: Jerry Van Kolken via Sprinklerforum 
<[email protected]>
Date: 12/5/19 7:10 PM (GMT-08:00)
To: [email protected]
Cc: [email protected]
Subject: Detached Garage


I’m a little rusty on my 13D.



I have a residence with a detached 3 car garage with a non-storage attic above 
about 860 sqft. If I’m to provide protect the structure would it still fall 
under 13d?



Jerry Van Kolken

Millennium Fire Protection Corp.

2950 San Luis Rey Rd.

Oceanside, CA 92058

(760) 722-2722 FX 722-2730



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to