That’s the same formula I had from an old ASCOA handbook dons ago. It’s very 
rough and dirty but generally works. 

Travis Mack, CFPS, CWBSP, RME-G, SET
480-505-9271 x700
MFP Design, LLC
www.mfpdesign,com
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

> On Dec 16, 2019, at 11:25 AM, Michael Hill via Sprinklerforum 
> <[email protected]> wrote:
> 
> 
> I have an old cutout from an AFSA Tech Talk… from August 1992 that gives a 
> pipe length formula.
>  
> A/6  x  B  =  Length of pipe that can be installed in open web bar joist.
>  
> A = Depth of bar joists (expressed in inches)
> B = Distance between bar joists (expressed in feet)
>  
> It is a general formula and does not necessarily mean every diameter of 
> determined length will work.
>  
> Mike Hill
>  
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Prahl, Craig/GVL via Sprinklerforum
> Sent: Monday, December 16, 2019 1:18 PM
> To: [email protected]
> Cc: Prahl, Craig/GVL <[email protected]>
> Subject: Routing pipe through bar joist - clearance issues
>  
> I’ve got a structural guy wanting to substitute bar joist for wide flange 
> steel.  The issue is clearance.  They just assumed if they provided bar joist 
> we could run our piping in the webs of the joist which would put us 1 – 5 ft 
> above the ceiling. 
>  
> The spacing between joists is unknown but could be “close”.
>  
> So the question, does anyone have any cheat sheets or spreadsheets showing 
> the maximum diameter of pipe based on a full length stick that can be routed 
> up within bar joist based on the bar joist spacing and depth?
>  
> Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 864.676.5252 | 
> [email protected] | www.jacobs.com
> 1041 East Butler Road   Greenville, South Carolina  29606
>  
>  
> 
> NOTICE - This communication may contain confidential and privileged 
> information that is for the sole use of the intended recipient. Any viewing, 
> copying or distribution of, or reliance on this message by unintended 
> recipients is strictly prohibited. If you have received this message in 
> error, please notify us immediately by replying to the message and deleting 
> it from your computer.
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org