I didn't know of the bevel washer. That will be handy in the future. Thank
you.

On Thu, Jan 2, 2020 at 10:35 AM Hinson, Ryan via Sprinklerforum <
[email protected]> wrote:

> Assuming you have done your homework regarding whether and at what hanger
> spacing the structure can support the weight of the water-filled pipe in
> accordance with NFPA 13; in my experience, one still cannot hang from the
> bottom lip of exposed Z-purlins and must instead hang with something like a
> Cooper B-Line #51 side beam bracket from the center 1/3 of the purlin spine
> with ½” nut, bolt, and washers to not void the listing of the support
> structure itself.  From the side beam bracket, a ½” rod hanging down with a
> nut and Figure B3234 bevel washer oriented such that the rod can hang
> straight down *without* lateral loading or bending since it is axially
> loaded vertically in the direction of gravity thus complying with NFPA 13
> (2019) Section 17.2.1.6 along with handbook commentary:
>
>
>
> *Threaded Sections of Rods.** Threaded sections of rods shall not be
> formed or bent.*
>
> *The requirement in 17.2.1.6 also applies to the rod once it is installed.
> Cracks can result if the rod is arranged with a lateral load applied to it.
> In other words, the rod must be axially loaded once it is connected between
> the building structure and the system pipe. Hanger attachments are
> available that are listed for attaching to the building structure and that
> can accommodate angles from vertical, allowing the rod to remain unbent.*
>
>
>
> I have seen many installations whose structural connections do not allow
> purely axial loading in the rod hangers and induce lateral loads in
> violation of this standard section.
>
>
>
> Don’t forget that ultimately, the structural member manufacturer (Butler
> in this case) must be consulted for allowable connection location means and
> methods regarding drilling of their engineered structural members.
>
>
>
> Good luck!
>
>
>
> *Ryan L. Hinson**, PE*, SET***  \  Burns & McDonnell
>
> Senior Fire Protection Engineer
>
> *O* 952-656-3662 \  *M* 320-250-5404  \  *F* 952-229-2923
>
> [email protected]  \  burnsmcd.com <http://www.burnsmcd.com/>
>
> 8201 Norman Center Drive, Suite 300  \  Bloomington, MN 55437
>
> *Registered in: LA, MD, MN, PA, TX, & UT
>
> **NICET IV - Water-Based Systems Layout
>
>
>
> *From:* Sprinklerforum <[email protected]> *On
> Behalf Of *James Litvak via Sprinklerforum
> *Sent:* Thursday, January 2, 2020 7:37 AM
> *To:* [email protected]
> *Cc:* James Litvak <[email protected]>
> *Subject:* Looking for a 6" hanger for sloped roof
>
>
>
> I'm trying to hang 6" pipe flat beneath a roof with a 4:12 slope, but
> having trouble finding an attachment. It's a standard Butler-style building
> with Z-purlins, and I'm hanging the pipe flat, both perpendicular and
> parallel to the slope. The Sammy hangers with swivels are not listed, and
> the slope is way too steep to "adjust" the rod. About the only thing I have
> been able to find is welded linked eye rods from Tolco (
> http://www.cooperindustries.com/content/dam/public/bline/Resources/Library/catalogs/pipe_hangers/pipe_hangers_and_supports/TA-EyeRod.pdf
> <https://nam05.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.cooperindustries.com%2Fcontent%2Fdam%2Fpublic%2Fbline%2FResources%2FLibrary%2Fcatalogs%2Fpipe_hangers%2Fpipe_hangers_and_supports%2FTA-EyeRod.pdf&data=02%7C01%7Crhinson%40burnsmcd.com%7Cbf61c7082e63425ad89308d78f88e034%7Cbfbb9a2b6d994e78b3c795005d555c8b%7C0%7C1%7C637135690352455044&sdata=zAKwLO4H566Pwcw88U0zCtwiFxCqPqgQYZ1%2FPCZcgxA%3D&reserved=0>).
> However, even though the Z-purlins are heavy gauge, it seems like a bad
> idea to hang from the bottom lip. In which case, even if I went with the
> linked eye rods, hanging from the side of the purlin seems like it would
> create its own difficulty. Does anyone here have a suggestion for how to
> hang in this situation? I also need to trapeze the pipe across the slope,
> but I figure whatever solution I can use to hang the pipe across the slope
> will also work for trapeze hangers.
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to