NFPA 13 (2016) Table 23.4.4.8.1 has it as 150 along with copper tube and brass.



Dale F. Wingard, SET
Designer Commercial/Marine Division
NICET IV #76284
Water-based Systems

Hiller Systems
A Division of The Hiller Companies, Inc.

3751 Joy Springs Drive
Mobile, AL 36693
o: 251.661.1275 ext. 10145
HillerFire.com

[Macintosh HD:Users:andrechiang:Dropbox:Emily's Files:Hiller:Email 
Signature:Hiller100 Email Signatures 2019-01-10:Hiller100 Email Signatures V1 
2019-01-10 - Systems.png]

Protecting life and property since 1919

From: Sprinklerforum <[email protected]> On Behalf 
Of Paul Cetani via Sprinklerforum
Sent: Tuesday, January 7, 2020 2:20 PM
To: [email protected]
Cc: Paul Cetani <[email protected]>
Subject: SS Pipe penetration into anechoic chamber friction loss

Happy new year sprinkler guru's,
I have attached a picture of a fabricated 1½" stainless steel pipe penetration 
that we are supposed to connect our sprinkler drops to (on the roof of) an 
Anechoic Chamber. The client also wants flexible drops. Without addressing the 
"listing" of this component, I am looking for a "C" factor for this. I have 
contacted the manufacturer (German company) but they do not have any friction 
loss data. Have any of you dealt with this before?
Thanks in advance for your input.

Paul B. Cetani
Nor Cal Fire, Inc.
[email protected]<mailto:[email protected]>