I have done multiple BIM projects. The other trades usually do not follow the 
model to a T as drawn for no justifiable reason that I have seen. BIM does work 
much better than traditional coordinating in my experience but I have not seen 
the savings in labor that would significantly justify the additional expense in 
design as of yet.

 

Just my opinion 

 

Greg McGahan

Genesis Fire Services, LLC

o-850-637-8535

 

From: Sprinklerforum <[email protected]> On Behalf 
Of Prahl, Craig/GVL via Sprinklerforum
Sent: Wednesday, January 15, 2020 2:36 PM
To: [email protected]
Cc: Prahl, Craig/GVL <[email protected]>; Travis Mack, SET, CFPS, CWBSP, 
RME-G <[email protected]>
Subject: RE: BIM Woes

 

We did REVIT design for a process building, 4 levels, 8 foam-water deluge 
systems, flow was 7600 gpm.

 

We coordinated with every discipline, every discipline worked together as the 
final product had to be certified clash free.  Contractors were instructed to 
NOT deviate from the design documents or any cost associated with their change 
was on their nickel.

 

Bids came in and were super close.  After it was all over I queried the 
sprinkler contractor to get his feedback on the package and installation.  He 
told me they chopped $200K out of the bid (winning bid was $1.4MM) that would 
have been allocated for unplanned rework.  They only had to reroute one section 
of pipe due to a field routed conduit bank that wasn’t modeled.  

 

When the design is done right and all participate, and the contractors are held 
to follow that design, BIM works. 

 

Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 864.676.5252 |  
<mailto:[email protected]> [email protected] |  
<http://www.jacobs.com/> www.jacobs.com

1041 East Butler Road   Greenville, South Carolina  29606

 

From: Sprinklerforum <[email protected] 
<mailto:[email protected]> > On Behalf Of Travis 
Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
Sent: Wednesday, January 15, 2020 3:05 PM
To: [email protected] 
<mailto:[email protected]> 
Cc: Travis Mack, SET, CFPS, CWBSP, RME-G <[email protected] 
<mailto:[email protected]> >
Subject: [EXTERNAL] RE: BIM Woes

 

Until our industry embraces this BIM fully, we will have these issues.  Steve 
nailed it.  When done correctly, it is great.  But we all have horror stories.  
Spend 6 months on 3D coordination and then no one follows the model.  Just had 
an issue today.  Fitter calls telling us we are hitting everything and that it 
is all wrong.  Well, we pull up the model and show we are where we indicated.  
Turns out mechanical guy didn’t follow the model and now the coordination 
process begins out in the field.  The is the same job where only 
fire/plumbing/duct are coordinating.  There are electrical and other trades 
that just said they weren’t participating.  So that project will be a total 
waste of time.

 

We have seen ones go very well when all are on board.  It all comes down to the 
strength of the 3D coordinator and the strength of the GC superintendent to 
enforce things.

 

 
<https://urldefense.com/v3/__http:/www.mfpdesign.com/__;!!B5cixuoO7ltTeg!SlIpmz3y4kCwmsF_R2FLu6Qlq1t9IeHldJTkDobZxXnIiI1A42NCTEUMhqsOf6QG6w$>
 

Travis Mack, CFPS, CWBSP, RME-G, SET

MFP Design, LLC

3356 E Vallejo Ct

Gilbert, AZ 85298

NEW EXTENSION: 480-505-9271 ext. 700

fax: 866-430-6107

 <mailto:[email protected]> [email protected]

www.mfpdesign.com 
<https://urldefense.com/v3/__http:/www.mfpdesign.com__;!!B5cixuoO7ltTeg!SlIpmz3y4kCwmsF_R2FLu6Qlq1t9IeHldJTkDobZxXnIiI1A42NCTEUMhqu8AmzB1A$>
 

 

Send large files to us via:  
<https://urldefense.com/v3/__https:/na01.safelinks.protection.outlook.com/?url=https*3A*2F*2Fwww.hightail.com*2Fu*2FMFPDesign&data=02*7C01*7C*7C1121d49f9e6b4cf248f108d4df580e77*7C14e5497c16da42e69ffa77d19bafe511*7C0*7C0*7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5*2BAZvlHhABSexWY*3D&reserved=0__;JSUlJSUlJSUlJSUlJSU!!B5cixuoO7ltTeg!SlIpmz3y4kCwmsF_R2FLu6Qlq1t9IeHldJTkDobZxXnIiI1A42NCTEUMhqu2ZsOBZw$>
 https://www.hightail.com/u/MFPDesign 

LinkedIn:  
<https://urldefense.com/v3/__https:/na01.safelinks.protection.outlook.com/?url=https*3A*2F*2Fwww.linkedin.com*2Fin*2Ftravismack&data=02*7C01*7C*7C1121d49f9e6b4cf248f108d4df580e77*7C14e5497c16da42e69ffa77d19bafe511*7C0*7C0*7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN*2BZodi*2FhbeCbHNRijI*3D&reserved=0__;JSUlJSUlJSUlJSUlJSUl!!B5cixuoO7ltTeg!SlIpmz3y4kCwmsF_R2FLu6Qlq1t9IeHldJTkDobZxXnIiI1A42NCTEUMhqsvH7XVNw$>
 https://www.linkedin.com/in/travismack

 

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

 

 

From: Matthew J Willis <[email protected] <mailto:[email protected]> 
> 
Sent: Wednesday, January 15, 2020 12:54 PM
To: [email protected] 
<mailto:[email protected]> 
Cc: Steve Leyton <[email protected] 
<mailto:[email protected]> >; 'Travis Mack, SET, CFPS, CWBSP, RME-G' 
<[email protected] <mailto:[email protected]> >; Michael Goodis 
<[email protected] <mailto:[email protected]> >
Subject: BIM Woes

 

Subject Change:

I really enjoy BIM discussions.

I call it BIM just to tick off T-Mack.

 

 

I have had, and am continuing to have good success.

 

Do they all work. No. Have I had tragedies, sure.

All parties have to be onboard for it to work.

 

It is always interesting because we are normally #11 or lower on the BIM 
hierarchy.

That is fine with me. I prefer to know where everyone is.

 

Keep in mind, you are 3 months behind when you get the job.

Mech/Elec/Others are already drawn.

 

Keep them where they are. Fight for your spot.

 

BIM is here. To stay.

 

R/

Matt

 

 

Matthew J. Willis, CWBSP

Design Manager /3-D Specialist

 
<https://urldefense.com/v3/__http:/rapidfireinc.com/__;!!B5cixuoO7ltTeg!SlIpmz3y4kCwmsF_R2FLu6Qlq1t9IeHldJTkDobZxXnIiI1A42NCTEUMhquTMBtIDw$>
 Rapid Fire Protection Inc.

1530 Samco Road

Rapid City, SD 57702

Office-605.348.2342

Direct Line-605.593.5063

Cell-605.391.2733

Fax:-605.348.0108

 



 

 

 

From: Sprinklerforum <[email protected] 
<mailto:[email protected]> > On Behalf Of Steve 
Leyton via Sprinklerforum
Sent: Wednesday, January 15, 2020 12:44 PM
To: [email protected] 
<mailto:[email protected]> 
Cc: Steve Leyton <[email protected] 
<mailto:[email protected]> >; 'Travis Mack, SET, CFPS, CWBSP, RME-G' 
<[email protected] <mailto:[email protected]> >; Michael Goodis 
<[email protected] <mailto:[email protected]> >
Subject: RE: [EXTERNAL] Pipe adjacent to duct

 

Thank you Michael, that's music to my ears. We started drawing sprinkler plans 
in Revit six years ago because that's what our clients wanted and what their 
clients were demanding. Since that time, the amount of effort that we expend in 
the construction administration phase of our projects has been reduced by at 
least a third, perhaps by half.  The fact is that BIM -not pretend NavisWorks 
BIM - but real parametric 3D drafting and coordination, does work and sometimes 
it works really well. Nothing's perfect, design and construction will never be 
fully in sync, but it's profoundly better. The fact that the fire sprinkler 
trade has mostly dismissed BIM as being of value is my bread and butter.

 

Party on Garth...

 

 

 

Steve Leyton  

 

(Sent from my phone; please excuse typos and voice text corruptions.)

 

 

 

 

-------- Original message --------

From: Michael Goodis via Sprinklerforum <[email protected] 
<mailto:[email protected]> > 

Date: 1/15/20 10:51 AM (GMT-06:00) 

To: [email protected] 
<mailto:[email protected]>  

Cc: Michael Goodis <[email protected] <mailto:[email protected]> >, "'Travis Mack, 
SET, CFPS, CWBSP, RME-G'" <[email protected] <mailto:[email protected]> > 

Subject: RE: [EXTERNAL] Pipe adjacent to duct 

 

Bim modeling, that’s funny. Never seen it work yet…. Only thing its been god 
for is (your duct is in the way, we see you cant move, the model is wrong, let 
now reroute due to the conflict, oh and wait, its not a CO because this should 
have been caught during the bim modeling.) 

 

Great stuff with the GC’s pushing it off to try and cut the change orders out. 
Gotta love it.

 

 

Michael Goodis     

Salesman, Project Manager

IL#000635   NICET#135586

Key Fire Protection Enterprises LLC

3200 Mike Padgett HWY

Augusta, GA 30906

Office- (706) 790-3473

Cell- (706) 220-8822

Fax: (706) 738-2119

 

 

 

From: Sprinklerforum <[email protected] 
<mailto:[email protected]> > On Behalf Of Travis 
Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
Sent: Wednesday, January 15, 2020 11:44 AM
To: [email protected] 
<mailto:[email protected]> 
Cc: Travis Mack, SET, CFPS, CWBSP, RME-G <[email protected] 
<mailto:[email protected]> >
Subject: RE: [EXTERNAL] Pipe adjacent to duct

 

Exactly.  It’s all up in the air.  It was a BIM job and not an issue with 
anyone during coordination.  Now it’s all up in the air installed and seems to 
be an issue.  You can’t win some days.  Plus, it shouldn’t be an issue at all, 
but now it is.

 

 
<https://urldefense.com/v3/__http:/www.mfpdesign.com/__;!!B5cixuoO7ltTeg!SlIpmz3y4kCwmsF_R2FLu6Qlq1t9IeHldJTkDobZxXnIiI1A42NCTEUMhqsOf6QG6w$>
 

Travis Mack, CFPS, CWBSP, RME-G, SET

MFP Design, LLC

3356 E Vallejo Ct

Gilbert, AZ 85298

NEW EXTENSION: 480-505-9271 ext. 700

fax: 866-430-6107

 <mailto:[email protected]> [email protected]

www.mfpdesign.com 
<https://urldefense.com/v3/__http:/www.mfpdesign.com__;!!B5cixuoO7ltTeg!SlIpmz3y4kCwmsF_R2FLu6Qlq1t9IeHldJTkDobZxXnIiI1A42NCTEUMhqu8AmzB1A$>
 

 

Send large files to us via:  
<https://urldefense.com/v3/__https:/na01.safelinks.protection.outlook.com/?url=https*3A*2F*2Fwww.hightail.com*2Fu*2FMFPDesign&data=02*7C01*7C*7C1121d49f9e6b4cf248f108d4df580e77*7C14e5497c16da42e69ffa77d19bafe511*7C0*7C0*7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5*2BAZvlHhABSexWY*3D&reserved=0__;JSUlJSUlJSUlJSUlJSU!!B5cixuoO7ltTeg!SlIpmz3y4kCwmsF_R2FLu6Qlq1t9IeHldJTkDobZxXnIiI1A42NCTEUMhqu2ZsOBZw$>
 https://www.hightail.com/u/MFPDesign 

LinkedIn:  
<https://urldefense.com/v3/__https:/na01.safelinks.protection.outlook.com/?url=https*3A*2F*2Fwww.linkedin.com*2Fin*2Ftravismack&data=02*7C01*7C*7C1121d49f9e6b4cf248f108d4df580e77*7C14e5497c16da42e69ffa77d19bafe511*7C0*7C0*7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN*2BZodi*2FhbeCbHNRijI*3D&reserved=0__;JSUlJSUlJSUlJSUlJSUl!!B5cixuoO7ltTeg!SlIpmz3y4kCwmsF_R2FLu6Qlq1t9IeHldJTkDobZxXnIiI1A42NCTEUMhqsvH7XVNw$>
 https://www.linkedin.com/in/travismack

 

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

 

 

From: Sprinklerforum <[email protected] 
<mailto:[email protected]> > On Behalf Of Prahl, 
Craig/GVL via Sprinklerforum
Sent: Wednesday, January 15, 2020 9:41 AM
To: [email protected] 
<mailto:[email protected]> 
Cc: Prahl, Craig/GVL <[email protected] <mailto:[email protected]> >; 
Travis Mack <[email protected] <mailto:[email protected]> >; David Bohannon 
<[email protected] <mailto:[email protected]> >; Matthew J Willis 
<[email protected] <mailto:[email protected]> >; 
[email protected] <mailto:[email protected]> 
Subject: RE: [EXTERNAL] Pipe adjacent to duct

 

Well it’s only a click of the mouse and it’s moved, so what’s your problem?   😉 

 

Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 864.676.5252 |  
<mailto:[email protected]> [email protected] |  
<http://www.jacobs.com/> www.jacobs.com

1041 East Butler Road   Greenville, South Carolina  29606

 

From: Sprinklerforum <[email protected] 
<mailto:[email protected]> > On Behalf Of Travis 
Mack via Sprinklerforum
Sent: Wednesday, January 15, 2020 11:34 AM
To: [email protected] 
<mailto:[email protected]> 
Cc: Travis Mack <[email protected] <mailto:[email protected]> >; 
[email protected] <mailto:[email protected]> ; Matthew J 
Willis <[email protected] <mailto:[email protected]> >; David 
Bohannon <[email protected] <mailto:[email protected]> >
Subject: Re: [EXTERNAL] Pipe adjacent to duct

 

Lol. That’s too funny. Everyone thinks fire sprinkler can just magically move. 

Travis Mack, CFPS, CWBSP, RME-G, SET

480-505-9271 x700

MFP Design, LLC

www.mfpdesign,com 
<https://urldefense.com/v3/__http:/www.mfpdesign,com__;!!B5cixuoO7ltTeg!SlIpmz3y4kCwmsF_R2FLu6Qlq1t9IeHldJTkDobZxXnIiI1A42NCTEUMhquB4cLC1g$>
 

Send large files to MFP Design via:

https://www.hightail.com/u/MFPDesign 
<https://urldefense.com/v3/__https:/www.hightail.com/u/MFPDesign__;!!B5cixuoO7ltTeg!Tdw2ycxMiEifeqPnNsaU3pOz4u4u_cZUe_St-0mFZXtsxNpCFWlsOvaona4GLVqxWQ$>
 

 

Sent from my iPhone

 

On Jan 15, 2020, at 9:23 AM, Matthew J Willis via Sprinklerforum 
<[email protected] 
<mailto:[email protected]> > wrote:

 

Hahahahaha

 

 

 

 

From: David Bohannon <[email protected] <mailto:[email protected]> > 
Sent: Wednesday, January 15, 2020 9:21 AM
To: [email protected] 
<mailto:[email protected]> 
Cc: Matthew J Willis <[email protected] <mailto:[email protected]> >; 
[email protected] <mailto:[email protected]> 
Subject: RE: [EXTERNAL] Pipe adjacent to duct

 

Just a question. If the duct is to close to the fire main why wouldn’t the duct 
have to move? Isn’t life safety more important than climate comfort?

Sent from AOL Mobile Mail
Get the new AOL app: mail.mobile.aol.com 
<https://urldefense.com/v3/__http:/mail.mobile.aol.com__;!!B5cixuoO7ltTeg!Tdw2ycxMiEifeqPnNsaU3pOz4u4u_cZUe_St-0mFZXtsxNpCFWlsOvaona7NH3VpRw$>
 

 

On Wednesday, January 15, 2020, John Denhardt via Sprinklerforum 
<[email protected] 
<mailto:[email protected]> > wrote: 

 

I am unaware of any language that would support the fire inspector’s position.

 

Thanks,

John

 

John August Denhardt, P.E.

Vice President Engineering and Technical Services

American Fire Sprinkler Association

301.343.1457 - Mobile

 

From: Sprinklerforum <[email protected] 
<mailto:[email protected]> > On Behalf Of Matthew 
J Willis via Sprinklerforum
Sent: Wednesday, January 15, 2020 10:00 AM
To: [email protected] 
<mailto:[email protected]> 
Cc: Matthew J Willis <[email protected] <mailto:[email protected]> >
Subject: RE: [EXTERNAL] Pipe adjacent to duct

 

Educate him.

 

Use your charm.

 

R/

Matt

 

From: Sprinklerforum <[email protected] 
<mailto:[email protected]> > On Behalf Of Travis 
Mack via Sprinklerforum
Sent: Wednesday, January 15, 2020 7:16 AM
To: [email protected] 
<mailto:[email protected]> 
Cc: Travis Mack <[email protected] <mailto:[email protected]> >; Prahl, 
Craig/GVL <[email protected] <mailto:[email protected]> >
Subject: Re: [EXTERNAL] Pipe adjacent to duct

 

No seismic. No insulation. 

Travis Mack, CFPS, CWBSP, RME-G, SET

480-505-9271 x700

MFP Design, LLC

www.mfpdesign,com 
<https://urldefense.com/v3/__http:/www.mfpdesign,com__;!!B5cixuoO7ltTeg!Tdw2ycxMiEifeqPnNsaU3pOz4u4u_cZUe_St-0mFZXtsxNpCFWlsOvaona7aUKCG7Q$>
 

Send large files to MFP Design via:

https://www.hightail.com/u/MFPDesign 
<https://urldefense.com/v3/__https:/www.hightail.com/u/MFPDesign__;!!B5cixuoO7ltTeg!Tdw2ycxMiEifeqPnNsaU3pOz4u4u_cZUe_St-0mFZXtsxNpCFWlsOvaona4GLVqxWQ$>
 

 

Sent from my iPhone

 

On Jan 15, 2020, at 7:12 AM, Prahl, Craig/GVL via Sprinklerforum 
<[email protected] 
<mailto:[email protected]> > wrote:

 

Could it be related to seismic movement of unrestrained ductwork against the FP 
pipe?

 

When you say ductwork, is that ½” between pipe and insulation or actual sheet 
metal?  

 

Craig Prahl | Jacobs | Group Lead/SME – Fire Protection | 864.676.5252 |  
<mailto:[email protected]> [email protected] |  
<http://www.jacobs.com/> www.jacobs.com

1041 East Butler Road   Greenville, South Carolina  29606

 

From: Sprinklerforum <[email protected] 
<mailto:[email protected]> > On Behalf Of Travis 
Mack via Sprinklerforum
Sent: Wednesday, January 15, 2020 8:54 AM
To: <[email protected] 
<mailto:[email protected]> > 
<[email protected] 
<mailto:[email protected]> >
Cc: Travis Mack <[email protected] <mailto:[email protected]> >
Subject: [EXTERNAL] Pipe adjacent to duct

 

We have a project where the fire inspector is stating that the fire sprinkler 
main is too close to ductwork.  There is a 6” main that is about 1/2” from the 
ductwork. 

 

Of course, the inspectors response is “it’s in the code book” when asking for a 
reference that mandates clearance to hvac ductwork. 

 

Has anyone run into something similar?

 

Note: this is not a high temp duct that would cause for enough heat to convert 
the sprinkler water to steam. This is just your standard, run of the mill, HVAC 
system. 

Travis Mack, CFPS, CWBSP, RME-G, SET

480-505-9271 x700

MFP Design, LLC

www.mfpdesign,com 
<https://urldefense.com/v3/__http:/www.mfpdesign,com__;!!B5cixuoO7ltTeg!Tdw2ycxMiEifeqPnNsaU3pOz4u4u_cZUe_St-0mFZXtsxNpCFWlsOvaona7aUKCG7Q$>
 

Send large files to MFP Design via:

https://www.hightail.com/u/MFPDesign 
<https://urldefense.com/v3/__https:/www.hightail.com/u/MFPDesign__;!!B5cixuoO7ltTeg!VcjF30iEaFuEx1cvHWPEx0GwlCXjsi62_q06GNj_cf6hxAEmmhx_JZyYbSEuPjBOcw$>
 

 

Sent from my iPhone

 

  _____  


NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
[email protected] 
<mailto:[email protected]> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 
<https://urldefense.com/v3/__http:/lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!Tdw2ycxMiEifeqPnNsaU3pOz4u4u_cZUe_St-0mFZXtsxNpCFWlsOvaona7JwYI3NA$>
 

_______________________________________________
Sprinklerforum mailing list
[email protected] 
<mailto:[email protected]> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 
<https://urldefense.com/v3/__http:/lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!Tdw2ycxMiEifeqPnNsaU3pOz4u4u_cZUe_St-0mFZXtsxNpCFWlsOvaona7JwYI3NA$>
 

_______________________________________________
Sprinklerforum mailing list
[email protected] 
<mailto:[email protected]> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 
<https://urldefense.com/v3/__http:/lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!B5cixuoO7ltTeg!Tdw2ycxMiEifeqPnNsaU3pOz4u4u_cZUe_St-0mFZXtsxNpCFWlsOvaona7JwYI3NA$>
 

 

  _____  


NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.

 

  _____  


NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
  • BIM Woes Matthew J Willis via Sprinklerforum
    • RE: BIM Woes Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
    • RE: BIM Woes Greg McGahan via Sprinklerforum

Reply via email to