Got a question with the 'apparently' all-encompassing dry standpipe air 
supervision requirement of NFPA 14 Section 6.1.1?:

  *   2013:

[cid:[email protected]]

  *   2016:

[cid:[email protected]]

  *   2019:
[cid:[email protected]]
Since it's illogical (to me) location has meaning, air pressure supervision 
appears required for both manual AND automatic dry standpipes.  Is this intent 
correct...even for a manual dry standpipe?  It seems to me that the dry 
standpipe supervision requirement should be coming from NFPA 14 based on the 
standpipe class and intended building use, not from 72.  Requiring air 
supervision could create prime conditions for intra-pipe corrosion for an 
otherwise normally-empty piping system.  Am I missing something?

Thanks,

Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell
Senior Fire Protection Engineer, Fire Protection Engineering Group
O 952-656-3662 \  NEW M 763-688-4045 \  F 952-229-2923
[email protected]<mailto:[email protected]>  \  
burnsmcd.com<http://www.burnsmcd.com/>
8201 Norman Center Drive, Suite 300  \  Bloomington, MN 55437

[cid:[email protected]]<https://www.linkedin.com/company/burns-&-mcdonnell>
  [cid:[email protected]] 
<https://www.facebook.com/BurnsMcDonnell>   
[cid:[email protected]] <https://twitter.com/BurnsMcDonnell>   
[cid:[email protected]] <https://www.youtube.com/user/burnsmcd>   
[cid:[email protected]] <http://www.burnsmcdblog.com/>   
[cid:[email protected]] 
<https://www.linkedin.com/profile/public-profile-settings?trk=prof-edit-edit-public_profile>
Proud to be one of FORTUNE's 100 Best Companies to Work For
Please consider the environment before printing this email.
*Registered in: LA, MD, MN, PA, TX, & UT
**NICET IV - Water-Based Systems Layout
This email and any attachments are solely for the use of the addressed 
recipients and
may contain privileged client communication or privileged work product. If you 
are not the
intended recipient and receive this communication, please contact the sender by 
phone at
816-333-9400, and delete and purge this email from your email system and 
destroy any
other electronic or printed copies. Thank you for your cooperation.
[Logo_1_Primary_2Color_sm]
Create Amazing.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to