According to my records, there has been a “3000 sq. ft. rule” as long as there have been area / density curves.
In the 1973 and 1974 editions, there was a note below Table 2-2.1(B) that said: For combustible construction with wet or dry system the minimum area of application shall be 3,000 sq. ft. Then for the 1975 edition the note was modified to say: For construction having unsprinklered combustible concealed spaces, the minimum area of sprinkler operation shall be 3,000 square feet. Best regards, Larry Keeping From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf Of Ron Greenman via Sprinklerforum Sent: March 4, 2020 3:30 PM To: sprinklerforum@lists.firesprinkler.org Cc: Ron Greenman <rongreen...@gmail.com> Subject: 3000 sqft rule Does anyone know what edition of 13 the 3000 sqft rule was introduced? Ron Greenman rongreen...@gmail.com<mailto:rongreen...@gmail.com> 253.576.9700 The Universe is monstrously indifferent to the presence of man. -Werner Herzog, screenwriter, film director, author, actor and opera director (1942-)