According to my records, there has been a “3000 sq. ft. rule” as long as there 
have been area / density curves.

In the 1973 and 1974 editions, there was a note below Table 2-2.1(B) that said:

               For combustible construction with wet or dry system the minimum 
area of application shall be 3,000 sq. ft.

Then for the 1975 edition the note was modified to say:

        For construction having unsprinklered combustible concealed spaces, the 
minimum area of sprinkler operation shall be 3,000 square feet.

Best regards,

Larry Keeping