What edition are you using? It is in the standard from 2013 and newer I 
believe. 

Travis Mack, CFPS, CWBSP, RME-G, SET
480-505-9271 x700
MFP Design, LLC
www.mfpdesign,com
Send large files to MFP Design via:
https://www.hightail.com/u/MFPDesign

Sent from my iPhone

> On Mar 9, 2020, at 8:27 AM, J H via Sprinklerforum 
> <[email protected]> wrote:
> 
> 
> I don't doubt their efficacy or necessity - my question is essentially how do 
> you calculate an area that is not required to be sprinklered by the standard 
> in the first place and does not meet w/ the definition of a compartment? I'll 
> just go ahead and do a four head calc for this balcony like I always do but I 
> was wondering what others were doing. My second thought would be to just size 
> the piping to the balcony sprinklers using the same interior pipe sizes 
> without calculating it as it's own compartment. We've had similar situations 
> arise when jurisdictions required limited attic protection in 13D systems and 
> didn't give any guidance on how to calculate the required quick response 
> sprinklers they were requiring at the ridge.
> 
>       Virus-free. www.avast.com
> 
>> On Fri, Mar 6, 2020 at 4:33 PM Bruce Verhei via Sprinklerforum 
>> <[email protected]> wrote:
>> 
>> https://www-dailyherald-com.cdn.ampproject.org/c/s/www.dailyherald.com/amp-article/20200221/news/200229736/
>> 
>> Balcony fire, spk head.
>> 
>>> On Mar 6, 2020, at 13:11, Pete Schwab via Sprinklerforum 
>>> <[email protected]> wrote:
>>> 
>>> We only calculate the single balcony in question.
>>> 
>>>  
>>> 
>>>  
>>> 
>>> Peter Schwab
>>> 
>>> VP of Purchasing and Engineering technologies
>>> 
>>>  
>>> 
>>> Wayne Automatic Fire Sprinklers Inc.
>>> 
>>> 222 Capitol Court
>>> 
>>> Ocoee, Fl 34761
>>> 
>>>  
>>> 
>>> Mobile: (407) 468-8248
>>> 
>>> Direct: (407) 877-5570
>>> 
>>> Fax: (407) 656-8026
>>> 
>>>  
>>> 
>>> www.waynefire.com
>>> 
>>>  
>>> 
>>> <image001.jpg>
>>> 
>>>  
>>> 
>>> <image002.png>
>>> 
>>>  
>>> 
>>> I sleep in a sprinklered home, do you?
>>> 
>>>  
>>> 
>>>  
>>> 
>>> From: Sprinklerforum <[email protected]> On 
>>> Behalf Of J H via Sprinklerforum
>>> Sent: Friday, March 6, 2020 3:52 PM
>>> To: [email protected]
>>> Cc: J H <[email protected]>
>>> Subject: How are you guys handling calcs for 13R balconies?
>>> 
>>>  
>>> 
>>> I was wondering how you guys are handling calculations for 13R balconies 
>>> since the sprinklers aren't even required per 13R but are mandated by the 
>>> IBC? Treating it as a compartment in this case means I have to do a 4 head 
>>> calc when the rest of the project only requires 2 heads calculated due to 
>>> compartmentalization. It's not a big deal but kind of a bummer when you can 
>>> have really small pipe sizes for a project if it weren't for those pesky 
>>> guys on the balcony!
>>> 
>>>  
>>> 
>>> J
>>> 
>>>  
>>> 
>>>  
>>> 
>>> 
>>> 
>>> Virus-free. www.avast.com
>>> 
>>>  
>>> 
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to