Kyle,

*disclaimer: I work for a company that sells air vents*

The short answer:
The in-line vent doesn’t work in fire sprinkler systems.

The long answer:
In a closed mechanical system there are generally two stages of air removal: 1) 
bulk air removal, which requires a simple ball valve (manual) or float valve 
(automatic) at a remote high point and 2) dissolved air removal, which requires 
an air scoop/expansion chamber or a vortex style air separator.

The removal of dissolved gases (gas molecules entrained in liquid water) is 
desirable in closed loop flowing systems. Because sprinkler systems are 
stagnant and the water entering the system contains approximately 10 ppm of 
dissolved oxygen (0.001% of water volume) the use of an expansion chamber at 
the beginning of the system provides no value.

Less than 1% of all oxygen available for corrosion in a sprinkler system is 
dissolved in the water when it enters the system. Attempts to “de-oxygenate” 
sprinkler water, either chemically or mechanically, are insignificant when 
looking at the bigger picture.

Thanks,
Lucas Kirn, PE

Engineered Corrosion Solutions
(314) 415-1387 | http://ecscorrosion.com

From: Kyle.Montgomery <[email protected]>
Sent: Monday, March 9, 2020 11:02 AM
To: [email protected]; [email protected]
Cc: Ben Young <[email protected]>
Subject: RE: [EXTERNAL] Re: Air Venting

How in the world would that work? I mean, the air is in the pipe when it’s 
installed, it doesn’t enter at a later date.

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Ben Young via Sprinklerforum
Sent: Friday, March 6, 2020 2:04 PM
To: [email protected]<mailto:[email protected]>; 
[email protected]<mailto:[email protected]>
Cc: Ben Young <[email protected]<mailto:[email protected]>>
Subject: [EXTERNAL] Re: Air Venting

The idea is to get out a majority of the trapped air but not every bit. So in 
your case you don't need to tie in every sprig and have multiple air vents, you 
could put it off one of the back sprigs but a remote branch line works too.

The other option is to use AGFs in line vent that you can put near the 
beginning of a system and it supposedly gets the air out before it has a chance 
to form pockets downstream. Haven't used one yet but they seem cool

On Fri, Mar 6, 2020 at 1:33 PM Bob Knight via Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 wrote:
In this case, the branch lines are all located beneath the trusses.  The 
trusses are shallow open web wood two feet on-center.  The elevation is 11’8” 
everywhere, so the sprigs are actually the highest points.  That said, it 
sounds like the air vent just needs to be at the furthest point that it can be.


Thank you,

Bob Knight, CET III
Fire by Knight, LLC
208-318-3057

From: Sprinklerforum 
[mailto:[email protected]<mailto:[email protected]>]
 On Behalf Of Steve Leyton via Sprinklerforum
Sent: Friday, March 06, 2020 10:52 AM
To: [email protected]<mailto:[email protected]>; 
[email protected]<mailto:[email protected]>
Cc: Steve Leyton
Subject: RE: Air Venting

I’d put it on a branch along the highest part of the building to which piping 
is attached, assuming that the piping more or less follows the roof contour.

SL

From: Sprinklerforum 
[mailto:[email protected]<mailto:[email protected]>]
 On Behalf Of Bob Knight via Sprinklerforum
Sent: Friday, March 06, 2020 9:21 AM
To: 
[email protected]<mailto:[email protected]>
Cc: Bob Knight
Subject: RE: Air Venting

Thanks Steve.  I get the high point part.   This system is all one elevation, 
but sprigs are being used.  Do I put the air vent on one of the sprigs, and is 
the most remote branch line the appropriate location?


Thank you,

Bob Knight, CET III
Fire by Knight, LLC
208-318-3057

From: Sprinklerforum 
[mailto:[email protected]<mailto:[email protected]>]
 On Behalf Of Steve Leyton via Sprinklerforum
Sent: Friday, March 06, 2020 10:17 AM
To: [email protected]<mailto:[email protected]>; 
[email protected]<mailto:[email protected]>
Cc: Steve Leyton
Subject: RE: Air Venting

Usually - and I mean to say, almost always – that’s going to be the high point 
of the system.  Trapped are generally migrates to the high point eventually.  
There are exceptions and some piping configuration can trap air in pockets that 
aren’t at the highest point of the system, but that’s usually where it is.


[cid:[email protected]]




From: Sprinklerforum 
[mailto:[email protected]<mailto:[email protected]>]
 On Behalf Of Bob Knight via Sprinklerforum
Sent: Friday, March 06, 2020 9:11 AM
To: 
[email protected]<mailto:[email protected]>
Cc: Bob Knight
Subject: Air Venting

Not being an air venting expert, when NFPA 13 (2016 ed.) says “The air venting 
valve should be located where it will be
most effective. System piping layout will guide the designer in choosing an 
effective location for venting. In order to
effectively accomplish venting, it is necessary to choose a location where the 
greatest volume of trapped air is vented
during the first fill and each subsequent drain and fill event (A.8.16.6).”

No other guidance is provided, so would this be at the most remote branch line, 
or at the end of a dead end main, or somewhere else?
Is there a “best practice” that is being used?

Thank you,

Bob Knight, CET III
Fire by Knight, LLC
208-318-3057
[FBK-LOGO-EMAIL]

_______________________________________________
Sprinklerforum mailing list
[email protected]<mailto:[email protected]>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwMFaQ&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=XBAfr8VvT_tqVmRgf4SS23R-L_XrkNqeFKnmzVeos0o&s=KKnRzmomHZu6jow9hSzsZThLbttz2R2r9rvIf1HsADE&e=>
--