I think you just have to add domestic if under 4".

Matt
On the road..

________________________________
From: Sprinklerforum 
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 on behalf of Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
Sent: Wednesday, March 18, 2020 11:32:04 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
Cc: Travis Mack, SET, CFPS, CWBSP, RME-G 
<tm...@mfpdesign.com<mailto:tm...@mfpdesign.com>>; 'Spencer Tomlinson' 
<spen...@tomlinsonfire.com<mailto:spen...@tomlinsonfire.com>>
Subject: RE: Minimum Lead-in Sizing


What is the reference for a minimum 4"?  We've had several smaller than that 
over my career.  Never had an issue that I know of.



[MFP_logo_F]<http://www.mfpdesign.com/>

Travis Mack, CFPS, CWBSP, RME-G, SET

MFP Design, LLC

3356 E Vallejo Ct

Gilbert, AZ 85298

NEW EXTENSION: 480-505-9271 ext. 700

fax: 866-430-6107

tm...@mfpdesign.com<mailto:tm...@mfpdesign.com>

www.mfpdesign.com<http://www.mfpdesign.com>



Send large files to us via: 
https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>

LinkedIn: 
https://www.linkedin.com/in/travismack<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>



"The bitterness of poor quality remains long after the sweetness of low price 
is forgotten."





From: Sprinklerforum 
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Spencer Tomlinson via Sprinklerforum
Sent: Wednesday, March 18, 2020 10:30 AM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Cc: Spencer Tomlinson 
<spen...@tomlinsonfire.com<mailto:spen...@tomlinsonfire.com>>
Subject: Minimum Lead-in Sizing



Hi all - I've got a customer that's in a pinch and I'm trying to help them out. 
 They have a 2" lead in supplying an existing building, mixed use 
commercial/residential.  NFPA 13 protection on 2 floors.  The 2" will actually 
calculate as it sits.  My question for those that have run into the "minimum 
pipe size is 4" requirement from an AHJ before, on a 13 system, what argument 
have you used to contradict the statement?



The ASTM standards listed in the underground piping tables of 13 for brass, 
copper, and stainless piping all include/cover pipe sizes smaller than 4".  
Section 23.4.1.3 (2016 edition) states that pipe sizing shall only be limited 
by available water supply.



Any other good arguments out there?



Spencer Tomlinson

Principal, PE



[red logo]

Ph:  316-202-6412

Fax: 316-202-2346

Cell: 620-955-7293

www.tomlinsonfire.com<http://www.tomlinsonfire.com/>


_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
  • Minimum Lead-in Si... Spencer Tomlinson via Sprinklerforum
    • RE: Minimum L... Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
      • Re: Minim... Matthew J Willis via Sprinklerforum
        • RE: M... Steve Leyton via Sprinklerforum
          • R... Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
            • ... Bruce Verhei via Sprinklerforum
      • RE: Minim... Steve Leyton via Sprinklerforum
        • RE: M... Spencer Tomlinson via Sprinklerforum
          • R... Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
            • ... Skyler Bilbo via Sprinklerforum
              • ... Matt Grise via Sprinklerforum
                • ... John Denhardt via Sprinklerforum
                • ... Steve Leyton via Sprinklerforum
            • ... Bob Knight via Sprinklerforum

Reply via email to