Perhaps they will accept what NFPA 13 states..

 

NFPA 13-2016 edition shows the size requirements

24.1.3* Size of Fire Mains.

24.1.3.1 Except as provided in 24.1.3.2 or 24.1.3.3, no pipe

smaller than 6 in. (150 mm) in diameter shall be installed as a

private service main.

24.1.3.2 For mains that do not supply hydrants, sizes smaller

than 6 in. (150 mm) shall be permitted to be used subject to

the following restrictions:

(1) The main supplies only automatic sprinkler systems, open

sprinkler systems, water spray fixed systems, foam systems,

or Class II standpipe systems.

(2) Hydraulic calculations show that the main will supply the

total demand at the appropriate pressure. Systems that

are not hydraulically calculated shall have a main at least

as large as the system riser.

24.1.3.3 Where a single main less than 4 in. (100 mm) in

diameter serves both fire systems and other uses, the non-fire

demand shall be added to the hydraulic calculations for the

fire system at the point of connection unless provisions have

been made to automatically isolate the non-fire demand during a fire event.

 

 

24.1.3.2 (2) above shows that hydraulic calculations can be used to lower
the pipe size.

 

Unless they have an ordinance that specifically changes this requirement
then they must go with what NFPA 13 states.

 

Anthony Carrizosa 

Project Manager | Fire Protection 

7855 S 206th St Kent, WA 98032

Cell: 206-679-5283 | Office: 253-872-7222 

 



https://archerconstruction.com
<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2farcherconstruction.com%
2f&c=E,1,Wdb65AWzMgSBzW3HDw91SfcRQCtxDUQKoJf-UowQ-WnB_WMosgG-8W7eLePJ42PwWQv
LiQx16Pls052VqwHO7tKm-_u5AnWly0ewkNiMkxn-AjQb1JI,&typo=1> 

 

 

 

From: Spencer Tomlinson <spen...@tomlinsonfire.com> 
Sent: Wednesday, March 18, 2020 12:09 PM
To: Travis Mack, SET, CFPS, CWBSP, RME-G <tm...@mfpdesign.com>; 'Steve
Leyton' <st...@protectiondesign.com>; sprinklerforum@lists.firesprinkler.org
Subject: RE: Minimum Lead-in Sizing

 

Some AHJ's have misinterpreted the tables in Chapter 10 of NFPA 13, because
the different standards listed give sizes of 4" -- ---___

 

Spencer Tomlinson

Principal, PE

 



Ph:  316-202-6412

Fax: 316-202-2346

Cell: 620-955-7293

www.tomlinsonfire.com <http://www.tomlinsonfire.com/> 

 

From: Travis Mack, SET, CFPS, CWBSP, RME-G <tm...@mfpdesign.com
<mailto:tm...@mfpdesign.com> > 
Sent: Wednesday, March 18, 2020 12:59 PM
To: Spencer Tomlinson <spen...@tomlinsonfire.com
<mailto:spen...@tomlinsonfire.com> >; 'Steve Leyton'
<st...@protectiondesign.com <mailto:st...@protectiondesign.com> >;
sprinklerforum@lists.firesprinkler.org
<mailto:sprinklerforum@lists.firesprinkler.org> 
Subject: RE: Minimum Lead-in Sizing

 

Where is he even reading a 4" minimum? I don't see that in NFPA 24 at all.
6" min if serving hydrants.  If serving sprinkler system, then must just
calc to prove.

 

 <http://www.mfpdesign.com/> 

Travis Mack, CFPS, CWBSP, RME-G, SET

MFP Design, LLC

3356 E Vallejo Ct

Gilbert, AZ 85298

NEW EXTENSION: 480-505-9271 ext. 700

fax: 866-430-6107

 <mailto:tm...@mfpdesign.com> tm...@mfpdesign.com

www.mfpdesign.com <http://www.mfpdesign.com> 

 

Send large files to us via:
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.highta
il.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C
14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2
wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
https://www.hightail.com/u/MFPDesign 

LinkedIn:
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linked
in.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%
7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7L
sZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>
https://www.linkedin.com/in/travismack

 

"The bitterness of poor quality remains long after the sweetness of low
price is forgotten."

 

 

From: Spencer Tomlinson <spen...@tomlinsonfire.com
<mailto:spen...@tomlinsonfire.com> > 
Sent: Wednesday, March 18, 2020 10:53 AM
To: Steve Leyton <st...@protectiondesign.com
<mailto:st...@protectiondesign.com> >;
sprinklerforum@lists.firesprinkler.org
<mailto:sprinklerforum@lists.firesprinkler.org> 
Cc: Travis Mack, SET, CFPS, CWBSP, RME-G <tm...@mfpdesign.com
<mailto:tm...@mfpdesign.com> >
Subject: RE: Minimum Lead-in Sizing

 

Yes sir - of the exact same opinion, as well as Matt's "what does it
matter"-  since it will calc without issue.  It's never been my opinion that
a minimum 4" is required anyway, since it's not explicitly stated, and the
only limitation on pipe sizing being explicitly stated in Chapter 23.  Was
hoping maybe one of the tech committee folks out there may share an
experience that a 4" minimum is not the intent, and it's just AHJ
misinterpretation by looking at ductile/cement lined/plastic pipe tables in
Chapter 10.  I've got what I need in the agreements from those that
responded - thanks as always!

 

Spencer Tomlinson

Principal, PE

 



Ph:  316-202-6412

Fax: 316-202-2346

Cell: 620-955-7293

www.tomlinsonfire.com <http://www.tomlinsonfire.com/> 

 

From: Steve Leyton <st...@protectiondesign.com
<mailto:st...@protectiondesign.com> > 
Sent: Wednesday, March 18, 2020 12:35 PM
To: sprinklerforum@lists.firesprinkler.org
<mailto:sprinklerforum@lists.firesprinkler.org> 
Cc: Travis Mack, SET, CFPS, CWBSP, RME-G <tm...@mfpdesign.com
<mailto:tm...@mfpdesign.com> >; Spencer Tomlinson <spen...@tomlinsonfire.com
<mailto:spen...@tomlinsonfire.com> >
Subject: RE: Minimum Lead-in Sizing

 

What TMack said.   "Please show me in the standard or code where that
provision resides."  Then show them the new listed in-building riser sweeps
from Ames that go down to 2".

 

SL

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org]
On Behalf Of Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
Sent: Wednesday, March 18, 2020 10:32 AM
To: sprinklerforum@lists.firesprinkler.org
<mailto:sprinklerforum@lists.firesprinkler.org> 
Cc: Travis Mack, SET, CFPS, CWBSP, RME-G <tm...@mfpdesign.com
<mailto:tm...@mfpdesign.com> >; 'Spencer Tomlinson'
<spen...@tomlinsonfire.com <mailto:spen...@tomlinsonfire.com> >
Subject: RE: Minimum Lead-in Sizing

 

What is the reference for a minimum 4"?  We've had several smaller than that
over my career.  Never had an issue that I know of.

 

 <http://www.mfpdesign.com/> 

Travis Mack, CFPS, CWBSP, RME-G, SET

MFP Design, LLC

3356 E Vallejo Ct

Gilbert, AZ 85298

NEW EXTENSION: 480-505-9271 ext. 700

fax: 866-430-6107

 <mailto:tm...@mfpdesign.com> tm...@mfpdesign.com

www.mfpdesign.com <http://www.mfpdesign.com> 

 

Send large files to us via:
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.highta
il.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C
14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2
wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
https://www.hightail.com/u/MFPDesign 

LinkedIn:
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linked
in.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%
7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7L
sZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>
https://www.linkedin.com/in/travismack

 

"The bitterness of poor quality remains long after the sweetness of low
price is forgotten."

 

 

From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org
<mailto:sprinklerforum-boun...@lists.firesprinkler.org> > On Behalf Of
Spencer Tomlinson via Sprinklerforum
Sent: Wednesday, March 18, 2020 10:30 AM
To: sprinklerforum@lists.firesprinkler.org
<mailto:sprinklerforum@lists.firesprinkler.org> 
Cc: Spencer Tomlinson <spen...@tomlinsonfire.com
<mailto:spen...@tomlinsonfire.com> >
Subject: Minimum Lead-in Sizing

 

Hi all - I've got a customer that's in a pinch and I'm trying to help them
out.  They have a 2" lead in supplying an existing building, mixed use
commercial/residential.  NFPA 13 protection on 2 floors.  The 2" will
actually calculate as it sits.  My question for those that have run into the
"minimum pipe size is 4" requirement from an AHJ before, on a 13 system,
what argument have you used to contradict the statement?  

 

The ASTM standards listed in the underground piping tables of 13 for brass,
copper, and stainless piping all include/cover pipe sizes smaller than 4".
Section 23.4.1.3 (2016 edition) states that pipe sizing shall only be
limited by available water supply.

 

Any other good arguments out there?

 

Spencer Tomlinson

Principal, PE

 



Ph:  316-202-6412

Fax: 316-202-2346

Cell: 620-955-7293

www.tomlinsonfire.com <http://www.tomlinsonfire.com/> 

 

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to