I always handle these situations in this manner: If I can’t find something in 
the code/standard to support my position, then I’m not going to be the one 
signing off on it.  If you have an FPE that is willing to sign off and take the 
liability for it, then let them make that call.  If the contractor customer is 
saying “we did it this way before,” that doesn’t carry the same weight.  

 

Again, not saying it won’t work.  But, what do you have to support your layout 
if something were to go wrong?

 

 <http://www.mfpdesign.com/> 

Travis Mack, CFPS, CWBSP, RME-G, SET

MFP Design, LLC

3356 E Vallejo Ct

Gilbert, AZ 85298

NEW EXTENSION: 480-505-9271 ext. 700

fax: 866-430-6107

 <mailto:tm...@mfpdesign.com> tm...@mfpdesign.com

www.mfpdesign.com

 

Send large files to us via:  
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
 https://www.hightail.com/u/MFPDesign 

LinkedIn:  
<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Ftravismack&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%2BZodi%2FhbeCbHNRijI%3D&reserved=0>
 https://www.linkedin.com/in/travismack

 

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

 

 

From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Richard Mote via Sprinklerforum
Sent: Thursday, March 19, 2020 5:34 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Richard Mote <spri...@aol.com>
Subject: Re: Spacing ESFR-17 Sprinkler at new interior wall

 

There are no obstructions to the spray pattern on the side away from the wall. 
Also was told the area immediately below the sprinkler in question is an 10' 
isle way for forklift travel with a steel guideway 2' away from the wall so the 
nearest possible storage is at least 8' away from the row of sprinklers in 
question and has a row of sprinklers directly over the end of the storage. 



-----Original Message-----
From: Pete Schwab via Sprinklerforum <sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org> >
To: Richard Mote <spri...@aol.com <mailto:spri...@aol.com> >; 
'sprinklerforum@lists.firesprinkler.org' 
<sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org> >
Cc: Pete Schwab <pe...@waynefire.com <mailto:pe...@waynefire.com> >
Sent: Thu, Mar 19, 2020 4:35 pm
Subject: RE: Spacing ESFR-17 Sprinkler at new interior wall

Just because someone “signed off” on it does not make it right.

In the event that there is a fire and a high dollar commodity is consumed (IE: 
Corona vaccine), and the special expert comes in and immediately sees a blatant 
code violation….. (Then again if it is an FM property and they approved they 
are the AHJ).

 

On the other hand, there has been recent testing for ESFR obstructions and I 
would present that as an equivalency. I personally feel what you have will work 
fine

 

Pete Schwab

 

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Richard Mote via Sprinklerforum
Sent: Thursday, March 19, 2020 6:25 PM
To: sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org> 
Cc: Richard Mote <spri...@aol.com <mailto:spri...@aol.com> >
Subject: Re: Spacing ESFR-17 Sprinkler at new interior wall

 

Just talked to the salesman that sold the job. He says that this room is 
identical to one adjacent to it and that the previous contractor (which did the 
original roof installation) did exactly as I was proposing. Don't think they 
were right but they are a 10 times bigger company than the one I am doing this 
project for. He basically told me to draw up something to submit. He was going 
to tell the installers to just duplicate what was already there. FM signed off 
on it so who am I to argue.

By the way I tried moving back up the line, but with 2'-6" between sprinkler 
and bar joist on each side, I was 5 sprinklers back and it still wasn't working 
out. 

 

-----Original Message-----
From: Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum 
<sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org> >
To: 'Richard Mote' <spri...@aol.com <mailto:spri...@aol.com> >; 
sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org> 
Cc: Travis Mack, SET, CFPS, CWBSP, RME-G <tm...@mfpdesign.com 
<mailto:tm...@mfpdesign.com> >
Sent: Thu, Mar 19, 2020 2:40 pm
Subject: RE: Spacing ESFR-17 Sprinkler at new interior wall

I’m not saying it won’t work.  But, there is nothing you have to hang your hat 
on should there ever be an issue.  I always tell customers to figure moving 3-5 
sprinklers on a branch line whenever you have a wall cause ESFR issues.  

 

 <http://www.mfpdesign.com/> 

Travis Mack, CFPS, CWBSP, RME-G, SET

MFP Design, LLC

3356 E Vallejo Ct

Gilbert, AZ 85298

NEW EXTENSION: 480-505-9271 ext. 700

fax: 866-430-6107

tm...@mfpdesign.com <mailto:tm...@mfpdesign.com> 

www.mfpdesign.com <http://www.mfpdesign.com/> 

 

Send large files to us via: https://www.hightail.com/u/MFPDesign 
<https://na01.safelinks.protection.outlook.com/?url=https%25253A%25252F%25252Fwww.hightail.com%25252Fu%25252FMFPDesign&data=02%25257C01%25257C%25257C1121d49f9e6b4cf248f108d4df580e77%25257C14e5497c16da42e69ffa77d19bafe511%25257C0%25257C0%25257C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%25252BAZvlHhABSexWY%25253D&reserved=0>
  

LinkedIn: https://www.linkedin.com/in/travismack 
<https://na01.safelinks.protection.outlook.com/?url=https%25253A%25252F%25252Fwww.linkedin.com%25252Fin%25252Ftravismack&data=02%25257C01%25257C%25257C1121d49f9e6b4cf248f108d4df580e77%25257C14e5497c16da42e69ffa77d19bafe511%25257C0%25257C0%25257C636379016677342180&sdata=tT5E7LsZjSmyreKi4gDCa70EWN%25252BZodi%25252FhbeCbHNRijI%25253D&reserved=0>
 

 

“The bitterness of poor quality remains long after the sweetness of low price 
is forgotten.”

 

 

From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org 
<mailto:sprinklerforum-boun...@lists.firesprinkler.org> > On Behalf Of Richard 
Mote via Sprinklerforum
Sent: Thursday, March 19, 2020 2:28 PM
To: sprinklerforum@lists.firesprinkler.org 
<mailto:sprinklerforum@lists.firesprinkler.org> 
Cc: Richard Mote <spri...@aol.com <mailto:spri...@aol.com> >
Subject: Spacing ESFR-17 Sprinkler at new interior wall

 

Have a job with existing ESFR-17 pendent sprinklers at the roof. Joist spacing 
is 5' oc with sprinklers centered between every other joist, thus 10' oc. The 
lines are on 10' centers so nice 100 sq. ft. per sprinkler. Tennent comes along 
and builds a room exactly 60' wide x  60' deep. Basically 1 bay wide x 1 column 
bay deep.  10" away from a row of sprinklers inside the room so no problem. 
However the row of sprinkler outside the room is now 8' away from the wall. If 
I plug and move that row of sprinklers 1'-4" away from the wall and then place 
a row 8' away toward the wall, the sprinklers adjacent to the wall are only 9¾" 
off the CL of the joist. My thinking is that since there is a wall 3 " away 
from the other side of the joist, spraying past the joist is not an issue. What 
say you?

 

Richard L. Mote, CET

Rimrock Design Services, LLC

P.O. Box 36

Middleburg, PA 17842

Ph. 928.821.8725 & 570.541.2685

Email: rimrock.design.servi...@gmail.com 
<mailto:rimrock.design.servi...@gmail.com> 

Web: https://rimrockdesignservices.com <https://rimrockdesignservices.com/> 

 

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org 
<mailto:Sprinklerforum@lists.firesprinkler.org> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org 
<mailto:Sprinklerforum@lists.firesprinkler.org> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
  • Spacing ESFR-17 Sp... Richard Mote via Sprinklerforum
    • RE: Spacing E... Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum
      • Re: Spaci... Richard Mote via Sprinklerforum
        • RE: S... Pete Schwab via Sprinklerforum
          • R... Richard Mote via Sprinklerforum
            • ... Travis Mack, SET, CFPS, CWBSP, RME-G via Sprinklerforum

Reply via email to