The Bracket IS the LAST hanger, per Flex manufacturers I have talked to,
but,
NFSA gave us an opinion that a 13" arm-over to a Flex still needs a hanger
if you are over 100 psi, 'cause that's what the book says.

*Jeff Garrison*
*248-331-6164 - cell*


On Fri, May 29, 2020 at 1:36 PM Dewayne Martinez via Sprinklerforum <
sprinklerforum@lists.firesprinkler.org> wrote:

> Thanks everyone for the input.  My fitter brought this up to me and after
> I read the sections I was still not sure.  John’s comment makes perfect
> sense.
>
>
>
> Thank you,
>
>
>
> Dewayne Martinez
>
> Fire Protection Design Manager
>
>
>
> *TOTAL* *Mechanical*
>
> *Building* *Integrity*
>
>
> W234 N2830 Paul Rd.
> Pewaukee, WI  53072
>
> dmarti...@total-mechanical.com
>
> Ph:  262-522-7110
>
> Cell: 414-406-5208
>
> http://www.total-mechanical.com/
>
>
>
>
>
> *From:* Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> *On
> Behalf Of *John Denhardt via Sprinklerforum
> *Sent:* Friday, May 29, 2020 10:41 AM
> *To:* sprinklerforum@lists.firesprinkler.org
> *Cc:* John Denhardt <jdenha...@firesprinkler.org>
> *Subject:* Re: NFPA 13, 2013 ed - hangers and pressures above 100psi
>
>
>
> In my opinion, no.  The flexible drop assembly is anchored to the
> ceiling.  The point of this requirement is to keep the pendent sprinkler
> from moving upwards during activation.  The flexible drop assembly
> accomplishes this requirement.
>
>
>
> Thanks,
>
> John
>
>
>
> John August Denhardt, PE
>
> *Vice President, Engineering and Technical Services*
>
> *American Fire Sprinkler Association*
>
> m: p:
>
> 301-343-1457
> 214-349-5965 ext 121
>
> w:
>
> firesprinkler.org
>
> <https://www.facebook.com/firesprinkler.org/>
> <https://twitter.com/afsa/status/1039528345367732224>
> <https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>
>    <https://www.instagram.com/firesprinklerorg/>
>
> *Help AFSA “Sound the Alarm” about sprinklers!*
>
> AFSA’s charitable partner the American Red Cross is educating millions
> through its Home Fire Preparedness Campaign. Help us support the inclusion
> of fire sprinklers in their messaging.  Donate today!
> <https://www.redcross.org/donate/cm/afsa-pub.html/>
>
>
>
>
>
> On Fri, May 29, 2020 at 11:28 AM Dewayne Martinez via Sprinklerforum <
> sprinklerforum@lists.firesprinkler.org> wrote:
>
> Is the hanger on the pipe supplying a flexible drop to a pendant sprinkler
> in a ceiling still required to one that prevents upward movement?
>
> Sections 9.2.3.4.4.1,9.2.3.5.2.2
>
>
>
> Thank you,
>
>
>
> Dewayne Martinez
>
> Fire Protection Design Manager
>
>
>
> *TOTAL Mechanical*
>
> *Building* *Integrity*
>
>
> W234 N2830 Paul Rd.
> Pewaukee, WI  53072
>
> dmarti...@total-mechanical.com
>
> Ph:  262-522-7110
>
> Cell: 414-406-5208
>
> http://www.total-mechanical.com/
>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>