Matt,

For what it’s worth (probably less than $0.02), I agree with you that it should 
provide an equivalent level of protection to be, say 5’-6” off of the wall as 
it would be if you were 11’-0” between sprinkler heads due to some obstruction. 
I suppose someone could make a strong argument that this isn’t true unless the 
next row of sprinkler heads is only 9’-0” away to create the average spacing of 
100 square feet.

But I agree with your premise, “how can it possibly be worse than if there was 
an obstruction present?” You’ve got to take some risks (i.e. “liability” 
oooooohhhh) sometimes because there are grey areas of the code open to 
interpretation. I say the goal of a successful organization is not to eliminate 
risk, it’s to decide what is the maximum they are willing to accept, and then 
get right up to it that limit. Unless you’re a consultant playing with someone 
else’s money. 😉

So, is this a grey area of the code that your willing to step into? Because I 
would be willing to bet that no one here can make a convincing argument that 
you are creating at deficient system by doing what you are describing. Although 
I’d like to hear more opinions.

-Kyle M


From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Matt Grise via Sprinklerforum
Sent: Friday, May 29, 2020 4:49 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Matt Grise <m...@afpsprink.com>
Subject: [EXTERNAL] Re: ESFR spacing

I may have mis-stated the scenario.

The sprinklers along the wall would be 5-0 from the wall as allowed by code. 
The next line of sprinklers would be 10-9 away, with 9' spacing along the line 
as allowed by code...if the line was moved to accommodate an obstruction. What 
the code is saying is literally that this setup would be allowed (safer?) if I 
went back and added an obstruction to force the line shift.

That does not seem logical. It sounds more like a quirk of the wording that was 
adopted when the code was written or perhaps an old "that's the way it was 
always done" similar to the system size limitations.

Clearly someone thought - and is willing to stand behind - the spacing if an 
obstruction is present. Would the system become less safe or non-code compliant 
if we went back and removed the obstruction after installation?

Matt
________________________________
From: Sprinklerforum 
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 on behalf of Skyler Bilbo via Sprinklerforum 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
Sent: Friday, May 29, 2020 6:18 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
Cc: Skyler Bilbo <sbi...@wenteplumbing.com<mailto:sbi...@wenteplumbing.com>>
Subject: Re: ESFR spacing

Any argument to what should be equivalent to the standard doesn't matter if the 
standard blatantly doesn't allow it (unless you are a PE and want to sign off 
on it, and get the AHJ to do so, as well).  Feel free to try and change the 
standard.

By your logic, you could take the small room rule, which would apply in a 16 ft 
x 50 ft room and say that it will also apply in a 31 ft by 50 ft room.  But it 
doesn't apply (the room is too big), even though the situation is similar.

I think the center of what you are trying to argue is that a fire that starts 
against a wall, as opposed to the middle of the room, between two lines of 
sprinklers, will set off fewer sprinklers, closer to the fire.  If you would 
like to pay for the testing, prove it out, and forever change how we space 
sprinklers off a wall, go ahead.  In the meantime, you cannot blatantly go 
against one very specific section of the standard (sprinkler spacing off a 
wall) by loosely applying a shift allowed for an obstruction between two rows 
of sprinklers.  If you do decide to try and change the standard, please make it 
so that we can apply the small room rule everywhere as well (9 feet off every 
wall!)...



Skyler Bilbo
[https://docs.google.com/uc?export=download&id=1Ot_QzTy6mc49_wnkJ-aKoPIBtkivO1gI&revid=0B1MzybbUMAWgNWRUNW03MkcyNkh4c0d4VXZMS0ZuQ2cvVzlFPQ]
1700 S. Raney Street
Effingham, IL 62401
217-819-6404 Direct
217-347-7315 Fax

sbi...@wenteplumbing.com<mailto:sbi...@wenteplumbing.com>
www.wenteplumbing.com<https://urldefense.proofpoint.com/v2/url?u=https-3A__linkprotect.cudasvc.com_url-3Fa-3Dhttp-253a-252f-252fwww.wenteplumbing.com-26c-3DE-2C1-2CkMBIvj0RHolH-5FCFu2no3qCz8YEWk16aumxKRlqwB5DNCS6zZmkuAddI-5FHsMwb2Ww4g1LroNROTCSc22nnMAlDagsicCiCl6aocnpCkJG-26typo-3D1&d=DwMF-g&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=jSTSLar-wqdPpelMfQPufoagJJdHyPYDkmx4Kb3d8qA&s=hAj3xDglAZm2HX231CR7RD7I6qGglnSwpzjXFr3EU7w&e=>

**new** 
www.beplumb.com<https://urldefense.proofpoint.com/v2/url?u=https-3A__linkprotect.cudasvc.com_url-3Fa-3Dhttp-253a-252f-252fwww.beplumb.com-26c-3DE-2C1-2CuTJVv8AeVanqKuHXzaFjI9wzzgZ3T8k29FQXIOkpP4RN00vYCMi7GG7gnnLkYho6yPQz0On9bm9xuNBFL1gcfFn4solxJFLH871aD-2DLiPlKB5A-2C-2C-26typo-3D1&d=DwMF-g&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=jSTSLar-wqdPpelMfQPufoagJJdHyPYDkmx4Kb3d8qA&s=a9MH1ZJud7ZNuV5fTfFrr7am-4XjpApVQV59GOlXu8M&e=>
Like us on facebook 
<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.facebook.com_justbeplumb&d=DwMF-g&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=jSTSLar-wqdPpelMfQPufoagJJdHyPYDkmx4Kb3d8qA&s=0ipsK8ly-jVAChUqBtS42FFHk4wAIHrlvEXzhJ8UtAQ&e=>
 for updates


On Fri, May 29, 2020 at 5:04 PM Matt Grise via Sprinklerforum 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
 wrote:

The situations causing the shift are not the same, but would the resulting 
protection level be the same or better? If it is ok to shift the sprinklers for 
an obstruction, is the protection less effective to shift without an 
obstruction?



Matt





From: Sprinklerforum 
<sprinklerforum-boun...@lists.firesprinkler.org<mailto:sprinklerforum-boun...@lists.firesprinkler.org>>
 On Behalf Of Skyler Bilbo via Sprinklerforum
Sent: Friday, May 29, 2020 4:58 PM
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Cc: Skyler Bilbo <sbi...@wenteplumbing.com<mailto:sbi...@wenteplumbing.com>>
Subject: Re: ESFR spacing



Matt,



My main concern with your application would be that the section you are 
referring to doesn't apply to the situation you are describing.  You can't 
apply a rule to spacing off a wall that is meant for offsetting a line due to 
an obstruction.  Two different sections/situations.  You say you are within the 
spacing rules, so your ceiling height must be under 30 feet (to allow up to 12 
foot spacing) and your protection area must be less than 100 square feet.  
Otherwise, it sounds like you will need to add a line of sprinklers.







Skyler Bilbo

[https://docs.google.com/uc?export=download&id=1Ot_QzTy6mc49_wnkJ-aKoPIBtkivO1gI&revid=0B1MzybbUMAWgNWRUNW03MkcyNkh4c0d4VXZMS0ZuQ2cvVzlFPQ]

1700 S. Raney Street

Effingham, IL 62401

217-819-6404 Direct

217-347-7315 Fax



sbi...@wenteplumbing.com<mailto:sbi...@wenteplumbing.com>

www.wenteplumbing.com<https://urldefense.proofpoint.com/v2/url?u=https-3A__linkprotect.cudasvc.com_url-3Fa-3Dhttp-253a-252f-252fwww.wenteplumbing.com-26c-3DE-2C1-2CfMOJw-2Du9vO1cg2hQ70XOiDVI5HOly82F-5FVAfD1uIna8ShJw4st0wpSq11Ktj3z-2DJgwCVem-2DHbVCX4I9PFqrsiwVUCVJz4oZoM-5FTAkMl0jZdRAfaWKW6Bcv1OYEmo-26typo-3D1&d=DwMF-g&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=jSTSLar-wqdPpelMfQPufoagJJdHyPYDkmx4Kb3d8qA&s=zXsQQjv9vyIf--zeclxvLOmewP75vmbPKq59ZL3qIAM&e=>



**new** 
www.beplumb.com<https://urldefense.proofpoint.com/v2/url?u=https-3A__linkprotect.cudasvc.com_url-3Fa-3Dhttp-253a-252f-252fwww.beplumb.com-26c-3DE-2C1-2C9gFtBXS3ytL8pTkU2xdZlYzI4c1hRGIkZu4MBn7vLI-5F4FxajPMdpBsvxfsyVi-2DNYlpiaOwZ-5FObRIGoRHpTTlOs0yZltoHH6X-5FSFW-5FABSaSO55Q-2C-2C-26typo-3D1&d=DwMF-g&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=jSTSLar-wqdPpelMfQPufoagJJdHyPYDkmx4Kb3d8qA&s=0FLJ1QLHmmVwAq0SYX4pev80pzXY__Tn64npJQFZMkc&e=>

Like us on facebook 
<https://urldefense.proofpoint.com/v2/url?u=http-3A__www.facebook.com_justbeplumb&d=DwMF-g&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=jSTSLar-wqdPpelMfQPufoagJJdHyPYDkmx4Kb3d8qA&s=0ipsK8ly-jVAChUqBtS42FFHk4wAIHrlvEXzhJ8UtAQ&e=>
 for updates





On Fri, May 29, 2020 at 4:33 PM Matt Grise via Sprinklerforum 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>
 wrote:

NFPA13 talks about shifting ESFR heads to avoid obstructions, but is there any 
concern with moving them when there is not an obstruction (within the spacing 
rules).



We have a situation where a small wall bump-out effectively spaces some ESFR 
heads over 10’, but less than 11’ – along with all of the other requirements. 
The spacing shift meets all of the NFPA 13 guidelines, except that there is no 
obstruction that causes it.



Are there any concerns with an application like that? It seems like it would 
perform as well or better than if there WAS an obstruction….



Thanks!



Matt



_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<https://urldefense.proofpoint.com/v2/url?u=https-3A__linkprotect.cudasvc.com_url-3Fa-3Dhttp-253a-252f-252flists.firesprinkler.org-252flistinfo.cgi-252fsprinklerforum-2Dfiresprinkler.org-26c-3DE-2C1-2C-5Fzw39OmJiH9r7e6B-5FXatZAmevw3-5FrqkeRLMZ-2DKk-2DzSrUSX7wNcjRDcaOykoMc-2D0ZLpUUKWyDODx3dT44C-2Djcq9CHQtQkiDQ0kh4kMAbkPwNLhYBK-26typo-3D1&d=DwMF-g&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=jSTSLar-wqdPpelMfQPufoagJJdHyPYDkmx4Kb3d8qA&s=suw3Omzja5wfedFsyYk6u3YVNSiOuZbCzC3Fvkb47XQ&e=>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<https://urldefense.proofpoint.com/v2/url?u=https-3A__linkprotect.cudasvc.com_url-3Fa-3Dhttp-253a-252f-252flists.firesprinkler.org-252flistinfo.cgi-252fsprinklerforum-2Dfiresprinkler.org-26c-3DE-2C1-2CErtP3kvUn4WC6C6J7XubmATTKXf-5FpfoZnquxBkmRssWegAtHAzm-2D7omLw0v-2DMDhYpyXmDv6em-5F9lCMikJU2kzZUtmt4-2DZ52dGBmDc8-2DfLQE-2C-26typo-3D1&d=DwMF-g&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=jSTSLar-wqdPpelMfQPufoagJJdHyPYDkmx4Kb3d8qA&s=6aiVP5xiqzj9-olLkCBs1lnYe1Wv0EoGHeDlgNlpyNY&e=>
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to