There are a lot of contingencies written into 7.14 that must also be met along 
with no prohibitions within chapters 11-43 so has all of that been looked at to 
be sure that sprinklers aren't required by other chapters?

Basically what 101 is describing sounds like a type of concealed space.

A.3.3.22.6 Normally Unoccupied Building Service
Equipment Support Area. Normally unoccupied building service support areas are 
often found in attics, crawl spaces, chases, and interstitial areas where the
space is vacant or intended exclusively for routing duct-work, cables, 
conduits, piping, and similar services and is rarely accessed. In such spaces, 
it is often difficult
or impossible to fully comply with the egress requirements of Chapter 7. Where 
portions of such spaces are routinely visited for storage, maintenance, 
testing, or
inspection, that portion is excluded from this definition, but the remainder of 
the space might be considered a normally unoccupied building service equipment 
support
area. Storage and fuel-fired equipment would not be expected to be permitted in 
these locations. Roofs are not considered to be normally unoccupied building
service equipment support areas

Craig Prahl | Jacobs | Group Lead/SME - Fire Protection | 864.676.5252 | 
craig.pr...@jacobs.com<mailto:craig.pr...@jacobs.com> | 
www.jacobs.com<http://www.jacobs.com/>
1041 East Butler Road   Greenville, South Carolina  29606

From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Larrimer, Peter A (HEFP\10NA5B) via Sprinklerforum
Sent: Tuesday, June 2, 2020 3:49 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Larrimer, Peter A (HEFP\10NA5B) <peter.a.larri...@va.gov>
Subject: [EXTERNAL] Exemption for sprinklers

NFPA 101, 7.14 (2018) permits sprinklers to be omitted from "Normally 
Unoccupied Building Service Equipment Support Areas".  These support areas are 
not intended to be accessed by persons for maintenance. However, they might 
have man-doors installed that would make them accessible and when they are over 
45,000 square feet, they are required to have man doors installed.

There is a provision in NFPA 101 that states the following:

7.14.2.2 Egress from normally unoccupied building service
equipment support areas shall be provided by doors complying
with 7.2.1 where the normally unoccupied building service
equipment support area exceeds 90,000 ft2 (8370 m2) in buildings
protected throughout by an approved, supervised automatic
sprinkler system in accordance with 9.7.1.1(1).

7.14.2.3 The absence of sprinklers in the normally unoccupied
building service equipment support area, as permitted by
an exemption of NFPA 13, shall not cause a building to be classified
as nonsprinklered for purposes of applying the provisions
of 7.14.2.2.


I am looking for the exemption in NFPA 13 that would allow a space to have 
man-doors, and also allow the sprinklers to be omitted from that space so that 
I can apply 7.14.2.3.  Can anyone help by showing me where that might exist in 
NFPA 13?  This provision was added to the 2012 edition of NFPA 101.

Thanks

Pete Larrimer
VA

________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to