I agree with John, but I will add some more information.  I have seen this
situation.  In my case, it came from IBC 2015, section 903.2.11.  "...the
basement shall be equipped throughout with an approved automatic sprinkler
system."   I would still have the same question you asked originally about
the stairs and elevator (after all, what does "equipped throughout" mean,
in this case).  As the installing contractor, I would get what that means
in writing from the Architect, and then from the AHJ (so that I don't find
out after the install is over that the AHJ disagrees with the Architect as
to what "equipped throughout" means).  Also, you may find out this
'basement only' protection is being driven by a different
section/requirement when you ask the Architect.

As a side note, I would bet that this 'basement only' requirement gets
missed more times than it is done right.  If you are in this profession,
and haven't seen this before, I strongly recommend a quick read of section
903.2.11 in IBC (same section in 2015 and 2018 versions).  What I am trying
to say is that this is a somewhat common scenario where sprinklers are
required to be installed, and they usually aren't.  It may be a good idea
to discuss this requirement with your local AHJ's the next time you chat
with them.


Good Luck,
Skyler Bilbo

1700 S. Raney Street
Effingham, IL 62401
217-819-6404 Direct
217-347-7315 Fax

[email protected]
www.wenteplumbing.com

**new** www.beplumb.com
Like us on facebook <http://www.facebook.com/justbeplumb>for updates


On Wed, Jun 10, 2020 at 11:57 AM John Denhardt via Sprinklerforum <
[email protected]> wrote:

> In my opinion, you are looking for direction from NFPA 13 where NFPA 13 is
> not applicable in this case.  Someone has decided to make a partial
> sprinklered building.  That person needs to tell you what sections of NFPA
> 13 are to be followed or ignored.  Otherwise, the liability falls on you.
> Do not let that happen
>
> Thanks,
> John
>
> John August Denhardt, PE
> *Vice President, Engineering and Technical Services*
>
> *American Fire Sprinkler Association*
> m: p: 301-343-1457
> 214-349-5965 ext 121
> w: firesprinkler.org
> <https://www.facebook.com/firesprinkler.org/>
> <https://twitter.com/afsa/status/1039528345367732224>
> <https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>
>    <https://www.instagram.com/firesprinklerorg/>
>
> *Help AFSA “Sound the Alarm” about sprinklers!*
>
> AFSA’s charitable partner the American Red Cross is educating millions
> through its Home Fire Preparedness Campaign. Help us support the inclusion
> of fire sprinklers in their messaging.  Donate today!
> <https://www.redcross.org/donate/cm/afsa-pub.html/>
>
>
> On Wed, Jun 10, 2020 at 12:07 PM Ed Kramer via Sprinklerforum <
> [email protected]> wrote:
>
>> I’m working on a small office building where only the basement is
>> required to be sprinklered.  Single-story with basement, VB construction.
>> I don’t know the code path that required basement-only to be sprinklered.
>>
>>
>>
>> This basement has 2 noncombustible 1-hour rated stairways that lead up to
>> the 1st floor.  Normally, we’d sprinkler the tops of these stairs.  For
>> a basement-only design, should the tops of these stairways be sprinklered?
>>
>>
>>
>> Project also has a hydraulic elevator.  I will be sprinklering the pit,
>> but the top of the shaft meets the criteria for omitting sprinklers, so
>> that’s not in question on this project.  But lets pretend the top is
>> required to be sprinklered - for a basement-only design, should the top of
>> the shaft be sprinklered?
>>
>>
>>
>> Thanks,
>>
>> Ed K
>>
>> Bamford Fire
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to