Subject: RE: Listed sprinkler guard for horizontal or vertical spray sidewalls


[EXTERNAL]

Thank you – a direct HIT!



SL



From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Dennis Wilson via Sprinklerforum
Sent: Wednesday, June 24, 2020 2:27 PM
To: [email protected]
Cc: Dennis Wilson <[email protected]>
Subject: RE: Listed sprinkler guard for horizontal or vertical spray sidewalls



Reliable F1FR-56



From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Steve Leyton via Sprinklerforum
Sent: Wednesday, June 24, 2020 4:21 PM
To: 
[email protected]<mailto:[email protected]>
Cc: Steve Leyton <[email protected]<mailto:[email protected]>>
Subject: Listed sprinkler guard for horizontal or vertical spray sidewalls



Does anyone know if any manufacturers have a listed guard for standard sidewall 
sprinklers?   We specified Viking on a project where the sprinklers are 
installed on the piping, running alongside beams in an open area of a tilt-up 
building that is being repurposed as a charter school, so Light Hazard 
occupancy class.   The client has requested that these particular sprinklers be 
protected from potential damage, but they are already installed so our first 
choice is to find a solution for horizontal sidewalls.   2nd choice is to roll 
the piping and install vertical sidewalls (I think we should have designed it 
that way in the first place in hindsight), so if no guards are available, at 
least the piping will protect the sprinklers.   Any of the manufacturers have a 
listed solution for horizontal or vertical?