1.  FM has Approval Standard 693 wherein some non-water based
fire-resistant hydraulic fluids are certified.

2.  There are tests for noncombustibility,  from ASTM, and they are cited
in NFPA 130 and NFPA 101.

3.  Approval using interpretation from the AHJ, which takes into
consideration occupancy and use.  Consider a long analogy and seque below,
which I apologize to the Forum in advance for.


The "Metro" standard deals with noncombustibility, because 'Metro
occupancies'  allow themselves in a non-simple, non-clear way to be
non-sprinklered, according to the NFPA committee members who do write to me.

We probably find such an admirable treatment of " noncombustibility"
within the covers of NFPA 130, the rail and rail / train station fire
design guide from NFPA, because they has such a miserable treatment of
sprinkler design and incongruency with their objective statement at Section
4.2.2.    Take a look at the admirable treatment of combustibility
prescriptions copy-pasted from the 2017 edition.

4.6* Noncombustible Material.
4.6.1* A material that complies with any of the following shall be
considered a noncombustible material: [ 101: 4.6.13.1]
(1) A material that, in the form in which it is used and under the
conditions anticipated, will not ignite, burn, support combustion, or
release …ammable vapors, when subjected to ‚re or heat. [ 101: 4.6.13.1(1)]
(2) A material that is reported as passing ASTM E136. [ 101: 4.6.13.1(2]
(3) A material that is reported as complying with the pass/fail criteria of
ASTM E136 when tested in accordance with the test method and procedure in
ASTM E2652. [ 101:4.6.13.1(3)]

More on judgment-with-uncertainty by fire plan reviewers.

The IBC and its handbook, quite emphatically writes,  "if you are an AHJ,
you are paid to render expert judgment.  There will be times this is
difficult and you will have to interpret the intent of the Building Code.
This is why we (insert your version of the Building Code here:
IBC/California Building Code/ Texas Building Code, etc.)  authorize the
Building Code Official and their duly appointed deputes with the trust and
expectation to interpret the intention of the Building Code.

I add to the above, for those AHJ that are paid civil servants, they are
government employees.  As far as I can recall, government is elected to
serve the people.  The definition of what is ' service'     changes with
the times and conditions, but service should be to ' the will of the
people'  in the instances of elected governments.  As such, it is the duty
of the AHJ to educate themselves, learn the intent of the Code, seek
advice, and then stand up and earn their money by making interpretations
that are open, honest and simple-as-possible.  It takes courage.  There
will be mistakes.  I don't know of any AHJ's being legally punished for
making mistakes, and there have been some deadly ones made in past,
repeatedly.  I know plenty of AHJ's that have been indirectly punished for
not serving the will of well-healed corporations whom financed the building
infrastructures.  That is the politics of plan review.

I have developed a tool that helps plan reviewers make
judgments-with-uncertainties, as all judgments involving safety measured
against Mother Nature, unavoidably involve uncertainty.  The burden of
uncertainty comes inherently with the territory of being a safety
professional.  If a plan reviewer wants to be 100% prescriptive... there is
AI coming.  As stated previously, AI already is replacing para-legals and
junior lawyers who pour over volumes of codes and records searchnig for
legal precedence.  When you think about it, a prescriptive design guide is
not much more than a big series of coded 'if - then ' statements.   AI can
search through all of our building safety references, standards and
Building Codes and come back with a prescriptive judgment  (if that is all
we are offering) before we can boot up our computer.  The future in plan
check, is executing judgment-with-uncertainty and field inspections.  Rote
reading of the Code and standards is not only a *DIS*service to the public,
and an indication that you may be overpaid as a safety professional  (or
overpaid as an entire organization, if that organization embraces a
structure too prescriptively oriented).  Being overly prescriptive is
setting oneself up for obsolescence and eventual replacement by
silicon-based neural networks.

I offer training to plan reviewers, with a tool I have developed, for
free.  It is numeric, falsifiable, open, honest, and somewhat simple (a
little bit of multiplication and addition involved). No jurisdiction on the
planet has expressed any interest in it.  Most fire plan reviewers are not
known for being 'overly curious' personalities.   And not too many people
are able to recognize something of value when they have not seen it
before... (how many of us bought into Microsoft, UPS or Amazon when we
first heard about them)?  Many in Code enforcement are anathema to
creatively evaluating new designs, Alternative Materials, or making
performance-based judgments.   This tool puts structure into the process,
while still asking for standup courageous decisions from not just the
reviewers, but justifiably from all stakeholders with skin in.   Due to
paragraph 2 of page 2 of NFPA design guides, I don't see where NFPA has
much skin in.  The tool asks questions that life safety professional are
paid to consider and render decisions upon (though precious few do in an
open, honest or simple manner).

" what are the worst-things that can happen?"  "
" how likely are these worst-case scenarios?"
" can we accept them?"

The last question is where not only courage comes in, but paradigm change.
If the plan reviewer has a story in their head that they can not accept
death from a design that they approve, then they have been reading the
wrong book.  Even prescriptive-based design and prescriptive codes
accept-in-their-designs, the chance of death from Mother Nature,
prescriptions just are not open or simple about this fact.  Sure,
prescriptive design may be fine from pursuit by legal-eagles, but even
prescriptive designs are never completely sure they are clear from the
talons of Mother Nature.

As the tool is offered for free, there is no vested monetary interest in
the above attempts to share information and improve good judgment in plan
checking...or design.

" Hominem unius libri timeo"   " Beware the person of but one book"
--Santo Tomas Aquinas

Scot Deal
Excelsior Risk & Fire Engineering
gms:  +420 606 872 129



On Fri, Jul 10, 2020 at 7:34 PM Steve Leyton via Sprinklerforum <
[email protected]> wrote:

> A client is wrestling with an AHJ regarding sprinkler exceptions in
> elevator pits on a multi-building project.  The issue is whether or not the
> hydraulic fluid is noncombustible and the MSDS sheet from Chevron states,
> “Not classified by OSHA as flammable or combustible.”   It’s NFPA rated 1
> for flammability (it’s basically mineral oil) with a flashpoint of 356°F
> and no Autoignition value is proffered.   NFPA 220 §4.1.5.1 has a
> definition but it’s for building materials – does anyone know if there’s an
> overarching (“preferred”) definition in the NFPA code set for
> “Noncombustible” as it applies to hydraulic elevator fluid?
>
>
>
>
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org