Ryan,
That was my thinking. We always us the restraining straps  on our hanger
assemblies.

Mike, 
The products I'm using are listed. This is a requirement from the client
side.



Jerry Van Kolken
Millennium Fire Protection Corp.
2950 San Luis Rey Rd.
Oceanside, CA 92058
(760) 722-2722 FX 722-2730

-----Original Message-----
From: Sprinklerforum <[email protected]> On
Behalf Of Hinson, Ryan via Sprinklerforum
Sent: Wednesday, August 26, 2020 11:11 AM
To: [email protected]
Cc: Hinson, Ryan <[email protected]>
Subject: RE: C-Clamp Hangers

Hanger attachments are being confused with bracing attachments.  
-       NFPA 13 (2019) Section 18.5.11.10 explicitly DOES NOT allow C-clamps
used for seismic bracing structural attachments with or         without
restraining straps unless specifically listed for such use. 
-       Section 18.7.1 allows their use for hangers in seismically active
areas when a restraining strap is included.  
-       Chapter 17 explicitly DOES allow listed use of c-clamps for hangers
alone.  

See commentary for further discussion and pictures depicting their allowed
hanger usage.

Hope this helps,

Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell Senior Fire Protection
Engineer O 952-656-3662 \  M 763-688-4045 \  F 952-229-2923
[email protected]  \  burnsmcd.com
8201 Norman Center Drive, Suite 500  \  Minneapolis-St. Paul, MN 55437
*Registered in: LA, MD, MN, PA, TX, & UT **NICET IV - Water-Based Systems
Layout



-----Original Message-----
From: Sprinklerforum <[email protected]> On
Behalf Of Jerry Van Kolken via Sprinklerforum
Sent: Wednesday, August 26, 2020 12:52 PM
To: [email protected]
Cc: [email protected]
Subject: C-Clamp Hangers

Does anyone know the reasoning Why you would not be allowed to use C-Clamps
for your hanger attachments? 

 

I've had a couple of specs have this requirement pass by my desk recently. 

 

Jerry Van Kolken

Millennium Fire Protection Corp.

2950 San Luis Rey Rd.

Oceanside, CA 92058

(760) 722-2722 FX 722-2730

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
https://nam05.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.fires
prinkler.org%2Flistinfo.cgi%2Fsprinklerforum-firesprinkler.org&amp;data=02%7
C01%7Crhinson%40burnsmcd.com%7C1d14008726f74fa34d4308d849e89359%7Cbfbb9a2b6d
994e78b3c795005d555c8b%7C0%7C0%7C637340610543326549&amp;sdata=%2Bt0YUDv8iKf9
xPab8hEUmLbdCBOX%2FIZ5VDKB7jaeLls%3D&amp;reserved=0
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to