On a standpipe system, I always indicate the FDC sign requirements on the shop 
drawing. I usually just state “CHARGE FDC AT 150 PSIG” unless the system needs 
more. 

John August Denhardt, P.E.
Vice-President Engineering and Technical Services
American Fire Sprinkler Association 
301-343-1457

> On Nov 25, 2020, at 11:48 AM, James Crawford via Sprinklerforum 
> <[email protected]> wrote:
> 
> Just throwing this out there, how many designers add a note to the drawings 
> indicating the signage required at the fire department connection indicating 
> the pressure required to deliver the standpipe system demand as per NFPA #14 
> section 6.4.5.2.2 (2016ed).
> 
> On a second note we have a building that is sprinklered and has a standpipe 
> and as such the standpipe demand when calculated is 63psi @ 500gpm at the top 
> most outlets, so the pressure required to deliver this is 112psi at the inlet 
> of the Siamese connection, this was what we put on the sign. I have been 
> advised that this is wrong and the pressure would be 149psi at the inlet as 
> this would then deliver 100psi at the hose valve.
> 
> Comments?
> 
> Thank You
> 
> James Crawford
> Phaser Fire Protection Ltd.
> Phone 604-888-0318
> Cel: 604-790-0938
> Email [email protected]<mailto:[email protected]>
> Web: www.phaserfire.ca<http://www.phaserfire.ca>
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to