Kevin,

Do FM data sheets now reflect results of these tests?

Best.

Bruce Verhei

> On 01/26/2021 2:02 PM Kevin Hall via Sprinklerforum 
> <sprinklerforum@lists.firesprinkler.org> wrote:
> 
>  
> There is an active FPRF project that addresses storage occupancies and
> sloped ceilings. It is currently in its third phase, and there has been
> some full scale testing at FM that I have witnessed. We might see some more
> options in the 2025 edition of the NFPA 13.
> 
> Kevin Hall, M.Eng, P.E., CWBSP, MSFPE
> *Coordinator, Engineering and Technical Services*
> 
> *American Fire Sprinkler Association*
> p: 214-349-5971
> w: firesprinkler.org
> <https://www.facebook.com/firesprinkler.org/>
> <https://twitter.com/afsa/status/1039528345367732224>
> <https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>
>    <https://www.instagram.com/firesprinklerorg/>
> 
> 
> *Expand your design department in 2021!*
> AFSA is taking its popular two-week Beginning Fire Sprinkler System
> Planning School on the road. From San Diego to Tampa Bay and stops in
> between, our technical experts will teach the basics of system layout based
> on the 2019 edition of NFPA 13. Space is limited. Enroll today at
> https://www.firesprinkler.org/schools
> 
> 
> On Tue, Jan 26, 2021 at 12:45 PM John Denhardt via Sprinklerforum <
> sprinklerforum@lists.firesprinkler.org> wrote:
> 
> > Steve is correct.  Protection schemes are available to some extent by
> > others; but currently not NFPA 13.  My only point was to respond to the 30%
> > increase due to slope as required by NFPA 13.  Engineering judgement or
> > other standards will need to be applied to those situations.
> >
> > The above is my personal opinion as a professional engineer.  It has not
> > been processed as a formal interpretation in accordance with the NFPA
> > Regulations Governing Committee Projects and should therefore not be
> > considered, nor relied upon, as the official position of the NFPA or its
> > Technical Committees.
> >
> > Thanks,
> > John
> >
> > John August Denhardt, PE
> > *Vice President, Engineering and Technical Services*
> >
> > *American Fire Sprinkler Association*
> > m: p: 301-343-1457
> > 214-349-5965 ext 121
> > w: firesprinkler.org
> > <https://www.facebook.com/firesprinkler.org/>
> > <https://twitter.com/afsa/status/1039528345367732224>
> > <
> > https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/
> > >
> >    <https://www.instagram.com/firesprinklerorg/>
> >
> > *Our members are at the heart of everything we do.*
> >
> >
> > *Expand your design department in 2021!*
> > AFSA is taking its popular two-week Beginning Fire Sprinkler System
> > Planning School on the road. From San Diego to Tampa Bay and stops in
> > between, our technical experts will teach the basics of system layout based
> > on the 2019 edition of NFPA 13. Space is limited. Enroll today at
> > https://www.firesprinkler.org/schools.
> >
> >
> > On Tue, Jan 26, 2021 at 12:38 PM Steve Leyton <st...@protectiondesign.com>
> > wrote:
> >
> > > I assume this statement of intent was added because full-scale fire
> > > testing has only been undertaken in test cells that have flat ceilings (I
> > > would very much appreciate input from the manufacturing community in that
> > > regard).  But that doesn't mean that we don't have to fire protect
> > storage
> > > under sloped roof assemblies because thousands of older buildings with
> > > saw-tooth and pitched roofs are used for S-group occupancies, and it
> > would
> > > be VERY helpful if there was some guidance on how to apply storage
> > > sprinklers under those conditions.   Whether it's in the standard (even
> > > annex material would be of value) or in the manufacturers' tech data
> > > sheets, we need SOMETHING, if only to substantiate so called "engineered"
> > > approaches to designs that will deliver adequate discharge to stored
> > > commodities below.    Simplistically disclaiming that there's no
> > > consideration given to a particular condition in the standard doesn't
> > mean
> > > that such a condition can't or doesn't exist.
> > >
> > > Definitely my opinion only,
> > >
> > > Steve L.
> > >
> > > -----Original Message-----
> > > From: Sprinklerforum [mailto:
> > > sprinklerforum-boun...@lists.firesprinkler.org] On Behalf Of John
> > > Denhardt via Sprinklerforum
> > > Sent: Tuesday, January 26, 2021 8:54 AM
> > > To: sprinklerforum@lists.firesprinkler.org
> > > Cc: John Denhardt <jdenha...@firesprinkler.org>
> > > Subject: Re: Area Increases
> > >
> > > As Travis stated, slope ceilings are not covered under the protection
> > > schemes of NFPA 13 for "Storage".  Thus, the increase does not apply to
> > > "Storage" unless miscellaneous or low-piled storage applies.
> > >
> > > NFPA 13 - 2019:  20.6.1 Ceiling Slope. The sprinkler system criteria
> > > specified in Chapters 20 through 25 are intended to apply to buildings
> > with
> > > ceiling slopes not exceeding 2 in 12 (16.7 percent) unless modified by a
> > > specific section in Chapters 20 through 25.
> > >
> > >
> > > *The above is my personal opinion as a professional engineer.  It has not
> > > been processed as a formal interpretation in accordance with the NFPA
> > > Regulations Governing Committee Projects and should therefore not be
> > > considered, nor relied upon, as the official position of the NFPA or its
> > > Technical Committees.*
> > >
> > > Thanks,
> > > John
> > >
> > > John August Denhardt, PE
> > > *Vice President, Engineering and Technical Services*
> > >
> > > *American Fire Sprinkler Association*
> > > m: p: 301-343-1457
> > > 214-349-5965 ext 121
> > > w: firesprinkler.org
> > > <https://www.facebook.com/firesprinkler.org/>
> > > <https://twitter.com/afsa/status/1039528345367732224>
> > > <
> > >
> > https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/
> > > >
> > >    <https://www.instagram.com/firesprinklerorg/>
> > >
> > > *Our members are at the heart of everything we do.*
> > >
> > > *Expand your design department in 2021!* AFSA is taking its popular
> > > two-week Beginning Fire Sprinkler System Planning School on the road.
> > From
> > > San Diego to Tampa Bay and stops in between, our technical experts will
> > > teach the basics of system layout based on the 2019 edition of NFPA 13.
> > > Space is limited. Enroll today at https://www.firesprinkler.org/schools.
> > >
> > >
> > >
> > > On Tue, Jan 26, 2021 at 11:16 AM Travis Mack via Sprinklerforum <
> > > sprinklerforum@lists.firesprinkler.org> wrote:
> > >
> > > > Slope >2:12 is not allowed for storage.  So, you don't apply because
> > > > it is not permitted.  Dry system increase - yes.
> > > >
> > > > If you are talking misc storage or low pile where you use the OH or EH
> > > > curve then yes, slope and dry increase.
> > > >
> > > >
> > > > Travis Mack, CFPS, CWBSP, RME-G, SET
> > > > Engineering Manager
> > > > MFP Design
> > > > 3356 E Vallejo Ct
> > > > Gilbert, AZ 85298
> > > > NEW EXTENSION: 480-505-9271 ext. 700
> > > > NEW MOBILE: 480-272-2471
> > > > mailto:travis.m...@mfpdesign.com
> > > > www.mfpdesign.com
> > > >
> > > >
> > > > From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org>
> > > > On Behalf Of JD Gamble via Sprinklerforum
> > > > Sent: Tuesday, January 26, 2021 9:13 AM
> > > > To: sprinklerforum@lists.firesprinkler.org
> > > > Cc: JD Gamble <jgam...@lssofsheridan.com>
> > > > Subject: Area Increases
> > > >
> > > > I know this answer is obvious before I even ask the question but for
> > > > some reason I am befuddled in brain lock (must be Monday again today)
> > > >
> > > > Do you have to apply the area increase for dry systems and sloped
> > > > ceilings to the area of operation for storage applications?
> > > >
> > > >
> > > > JD Gamble
> > > > LSS of Sheridan, Inc.
> > > > _______________________________________________
> > > > Sprinklerforum mailing list
> > > > mailto:Sprinklerforum@lists.firesprinkler.org
> > > >
> > > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > > > er.org
> > > >
> > > > _______________________________________________
> > > > Sprinklerforum mailing list
> > > > Sprinklerforum@lists.firesprinkler.org
> > > >
> > > > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> > > > er.org
> > > >
> > > _______________________________________________
> > > Sprinklerforum mailing list
> > > Sprinklerforum@lists.firesprinkler.org
> > >
> > >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> > >
> > _______________________________________________
> > Sprinklerforum mailing list
> > Sprinklerforum@lists.firesprinkler.org
> >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> >
> _______________________________________________
> Sprinklerforum mailing list
> Sprinklerforum@lists.firesprinkler.org
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org