If it's not a concrete tee, then I don't think you're going to be able to 
exceed 22" from the deck.

-Kyle M

-----Original Message-----
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Dennis Wilson via Sprinklerforum
Sent: Monday, February 1, 2021 3:08 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Dennis Wilson <dwil...@blackhawksprinklers.com>; Dale Wingard 
<dwing...@hillercompanies.com>
Subject: [EXTERNAL] RE: Pan-Type Construction

Around 20", so the deflector is over 22" the top of the pans.
But only 4" below the stems.

-----Original Message-----
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Dale Wingard via Sprinklerforum
Sent: Monday, February 1, 2021 4:03 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Dale Wingard <dwing...@hillercompanies.com>
Subject: RE: Pan-Type Construction

I am picturing a concrete waffle pattern.  What is the depth of the pan?

Regards,

Dale F. Wingard, SET
Designer Commercial/Marine Division
NICET IV #76284
Water-based Systems

Hiller Systems
A Division of The Hiller Companies, Inc.

3751 Joy Springs Drive
Mobile, AL 36693
c: 251.509.7108
o: 251.661.1275 ext. 10145
HillerFire.com



Protecting life and property since 1919


-----Original Message-----
From: Sprinklerforum <sprinklerforum-boun...@lists.firesprinkler.org> On Behalf 
Of Steve Leyton via Sprinklerforum
Sent: Monday, February 1, 2021 4:00 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Steve Leyton <st...@protectiondesign.com>; Dennis Wilson 
<dwil...@blackhawksprinklers.com>
Subject: RE: Pan-Type Construction

Do you mean Tee or Double-Tee construction?    Pan slabs are PIP, with and 
without metal decks, smooth ceiling by definition.

Steve L.   

-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Dennis Wilson via Sprinklerforum
Sent: Monday, February 01, 2021 1:52 PM
To: sprinklerforum@lists.firesprinkler.org
Cc: Dennis Wilson <dwil...@blackhawksprinklers.com>
Subject: Pan-Type Construction

Would anyone know what the maximum depth is allowed in concrete pan-type 
construction?
I have a job with exist. sprinklers installed along the bottom of the  stems 
with pendents.
The AHJ is questioning whether sprinklers are needed in each pocket.
Pockets are around 6' square w/ 8" wide stems both directions.

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.proofpoint.com/v2/url?u=https-3A__nam02.safelinks.protection.outlook.com_-3Furl-3Dhttp-253A-252F-252Flists.firesprinkler.org-252Flistinfo.cgi-252Fsprinklerforum-2Dfiresprinkler.org-26amp-3Bdata-3D04-257C01-257Cdwilson-2540blackhawksprinklers.com-257C33b42d80fb1d42f8d2ea08d8c6fd1ba7-257C20b3eafa18334148b9c58e75b45c105a-257C1-257C0-257C637478137681329414-257CUnknown-257CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0-253D-257C3000-26amp-3Bsdata-3D8mzxfwL-252F8WwAb-252BhcaWXdGkQkEUJoyXR3ZOWrDakFX6A-253D-26amp-3Breserved-3D0&d=DwICAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=1ypHaKFKrGDyg6VnUrVhq8FaSZzKWT5gvzE8Vn2RsGc&s=6BL03gwbOQVs6LjvVNy_FnVpWnwdd8BdKA7SG0Plnmo&e=
 
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.proofpoint.com/v2/url?u=https-3A__nam02.safelinks.protection.outlook.com_-3Furl-3Dhttp-253A-252F-252Flists.firesprinkler.org-252Flistinfo.cgi-252Fsprinklerforum-2Dfiresprinkler.org-26amp-3Bdata-3D04-257C01-257Cdwilson-2540blackhawksprinklers.com-257C33b42d80fb1d42f8d2ea08d8c6fd1ba7-257C20b3eafa18334148b9c58e75b45c105a-257C1-257C0-257C637478137681329414-257CUnknown-257CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0-253D-257C3000-26amp-3Bsdata-3D8mzxfwL-252F8WwAb-252BhcaWXdGkQkEUJoyXR3ZOWrDakFX6A-253D-26amp-3Breserved-3D0&d=DwICAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=1ypHaKFKrGDyg6VnUrVhq8FaSZzKWT5gvzE8Vn2RsGc&s=6BL03gwbOQVs6LjvVNy_FnVpWnwdd8BdKA7SG0Plnmo&e=
 
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.proofpoint.com/v2/url?u=https-3A__nam02.safelinks.protection.outlook.com_-3Furl-3Dhttp-253A-252F-252Flists.firesprinkler.org-252Flistinfo.cgi-252Fsprinklerforum-2Dfiresprinkler.org-26amp-3Bdata-3D04-257C01-257Cdwilson-2540blackhawksprinklers.com-257C33b42d80fb1d42f8d2ea08d8c6fd1ba7-257C20b3eafa18334148b9c58e75b45c105a-257C1-257C0-257C637478137681339370-257CUnknown-257CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0-253D-257C3000-26amp-3Bsdata-3Dp2LDsgFL-252BaFr8jcjO-252FCzJcDL6y52lXWJOOEo8uXum8c-253D-26amp-3Breserved-3D0&d=DwICAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=1ypHaKFKrGDyg6VnUrVhq8FaSZzKWT5gvzE8Vn2RsGc&s=BA7gw8I8V-6JF7eQwbxcJrzBZJt-hSh8Tqz6g0N0Vhc&e=
 
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
https://urldefense.proofpoint.com/v2/url?u=http-3A__lists.firesprinkler.org_listinfo.cgi_sprinklerforum-2Dfiresprinkler.org&d=DwICAg&c=wn3mZQLIuInh2ClcJ0_DIA&r=Z_2A85VL7AQzoqudh6uOyS3bn8etxB7nLN8OBJwQd9A&m=1ypHaKFKrGDyg6VnUrVhq8FaSZzKWT5gvzE8Vn2RsGc&s=mp7avJDFrH8D87f9DnRvujLXNBjv0QVKV-0QgqlvGfA&e=
 
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to