Actually, the coating would be allowed under the equivalency clause with
approval of the AHJ.

With AHJ approval, the 3000 sq ft rule could also be ignored.  Some years
ago, I made the mistake of saying no to this question while doing
interpretations for NFPA as a consultant and almost got them sued over my
response - so I know this answer really well....

Bob Caputo

On Wed, Feb 10, 2021 at 11:44 AM tstone52--- via Sprinklerforum <
[email protected]> wrote:

> Project is a 100 year old 6 story Steel & Concrete Hotel building. The roof
> is steel framed with concrete above and the Sixth floor ceiling is Plaster
> over metal lath. Over the years the building has been added onto with wood
> framing above the Sixth floor ceilings.
>
> As Part of a major renovation started in 2020, the installation of a
> complete NFPA 13 sprinkler system and Standpipes is taking place.
>
>
>
> A few substantial combustible concealed spaces have been discovered
> throughout the building on other floors too. If nothing is done the
> sprinkler design areas would need to be increased to 3,000 SF as outlined
> in
> Chapter 11.2.3.1.5. The sprinkler contractor and I have suggested filling
> these spaces with noncombustible Insulation.
>
>
>
> The architect and builder are discussing Flame Retardant Coating to be
> applied to the wood framing in order meet the Non-Combustible and Limited
> Combustible concealed space definition. In reviewing Chapter 11.2.3.1.5.2 I
> don't see where Flame Retardant Coating is an option in order to reduce the
> design area.
>
>
>
> I believe In order to reduce the Design areas these combustible spaces need
> to be filled with noncombustible Insulation.
>
>
>
> Would "Flame Retardant Coating" be considered an option as outlined in
> A.8.15.1.2.11 (commentary text) the equivalency provisions in Section 1.5?
>
>
>
> Thank you for your imput.
>
>
>
> Regards,
>
> G. Tim Stone
>
>
>
> G. Tim Stone Consulting, LLC
>
> NICET Level III Engineering Technician
>
> Fire Protection Sprinkler Design
>
> and Consulting Services
>
>
>
>    117 Old Stage Rd. - Essex
> <https://www.google.com/maps/search/117+Old+Stage+Rd.+-+Essex?entry=gmail&source=g>
> Jct., VT. 05452
>
> CELL: (802) 373-0638   TEL: (802) 434-2968
>
>               <mailto:[email protected]> [email protected]
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to