Joe,

While the AHJ is referring to 11.1.2, see NFPA 13 (2016)23.4.4.2.4.  The annex 
provides for the steps to increase the flow.

Jack W. Carlson, SET

-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Joe Burtell via Sprinklerforum
Sent: Thursday, February 11, 2021 12:47 PM
To: [email protected]
Cc: Joe Burtell <[email protected]>
Subject: Multiple System Calculation

I have a situation where an engineer is telling me I have to calculate a wet 
and dry system together because neither space meets the 1500 s.f minimum. I 
have a penthouse mechanical room OH 1 (WET) of 1014 s.f. and an adjacent room 
OH1 (DRY) of 469 s.f. I have calculated each room separate of each other. There 
is a full-height wall with a door that separates the rooms. The wall and door 
are not fire rated, so the large room method is out. This does not make any 
sense to me. Any sections that would require this to be done. He is saying 
11.1.2 of NFPA 13 2016 requires it. I argue exception #2 says it does not apply.

Best regards,

*Joe Burtell, SET, CFPS*

[image: Burtell Fire_Small]

Phone | Fax | Mobile| Text *406-204-4653 <++1-406-204-4653>*

116 N. 11th Street | Billings, MT 59101

Email: [email protected]

Web Site: http://www.burtellfire.com

*“**The bitterness of poor quality remains long after the sweetness of low 
price is forgotten.**”*

*NOTICE:*  The information contained in this e-mail transmission is intended 
only for use of the individual or entity named above.  This e-mail 
transmission, and any documents, files, previous e-mail transmissions or other 
information attached to it, may contain confidential information that is 
legally privileged.  If you are not the intended recipient of this e-mail 
transmission, or the employee or agent responsible for delivering it to the 
intended recipient, you are hereby notified that any disclosure, dissemination, 
distribution, copying or other use of this transmission or any of the 
information contained in or attached to this e-mail is strictly prohibited.  If 
you have received this e-mail transmission in error, please immediately notify 
us by return e-mail transmission and destroy the original e-mail transmission 
as well as its attachments without reading or saving it in any manner.  Thank 
you.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to