I would offer that there is no exception in the NFPA 14 standard for protection 
of piping serving horizontal exits and as you noted, those are different from 
the intermediate ones.   The distinction exists in both the standard and the 
IBC, which also requires the protection of piping.   Additionally, many fire 
departments aren't interested in those intermediates because they train so 
rigidly on FF operations staged in stairwells and vestibules.   Being a 
CA-based company, we're used to restrictive code amendments and fire department 
ordinances that tweak the standards, so I've encountered more restrictive 
(i.e., yes the intermediates are required AND they must be wrapped in 
fire-rated construction) and more relaxed (intermediate standpipes aren't 
required at all) policies.   


The foregoing is my opinion only and does not represent NFPA or the NFPA 14 
Technical Committee, nor intended to serve as an interpretation of the standard.

Steve Leyton
Protection Design & Consulting
San Diego, CA 





-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Matt Grise via Sprinklerforum
Sent: Monday, February 22, 2021 2:31 PM
To: [email protected]
Cc: Matt Grise <[email protected]>
Subject: standpipe protection

2016 edition of NFPA 14 section 6.1.2.2.4 says "where additional standpipes are 
needed to meet travel distance requirements in non-high-rise buildings, 
protection of piping is not required."

Is that intended to apply to standpipes near horizontal exits also? If they 
were closer to the stairs, they would not be needed. So technically they are 
there in order to meet travel distance requirements... so, no fire rated 
enclosure required?

Matt

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
  • standpipe protection Matt Grise via Sprinklerforum
    • RE: standpipe protection Steve Leyton via Sprinklerforum

Reply via email to