BTW, I probably should have included in my comments, the requirements for floor
control valve assemblies in NFPA 13, 2019 edition section 16.9.11, which might
be applicable to Jerry’s situation. Again, I may have missed the point of the
original question…. But I’m old so I have an excuse!
Bob Caputo, CFPS
President
American Fire Sprinkler Association
p: 214-349-5965 ext124
w: firesprinkler.org <http://firesprinkler.org/>
<https://www.facebook.com/firesprinkler.org/>
<https://twitter.com/afsa/status/1039528345367732224>
<https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>
<https://www.instagram.com/firesprinklerorg/>
Expand your business with ITM
Professionalize the role of your inspection team with AFSA’s ITM Inspector
Development Program. This comprehensive 20-month program provides a blended
learning environment teamed with robust curriculum created by top industry
leaders. Plus, the first six-months of instruction is online. Now enrolling for
Spring 2021 <https://www.firesprinkler.org/itm>.
> On Mar 18, 2021, at 9:35 PM, BRUCE VERHEI via Sprinklerforum
> <[email protected]> wrote:
>
> I’d ask why. Is the fire sprinkler system acting as detection system for a
> smoke exhaust system?
>
> Best.
>
> Bruce Verhei
>
>
>> On 03/18/2021 8:05 PM Travis Mack via Sprinklerforum
>> <[email protected]> wrote:
>>
>>
>> We've had cases where the 2 story volume area is required to be protected
>> from the 1st floor system, but not the entire building just off of one
>> system because of that.
>>
>> Travis Mack, CFPS, CWBSP, RME-G, COC, SET
>> Engineering Manager
>> MFP Design
>> 3356 E Vallejo Ct
>> Gilbert, AZ 85298
>> 480-505-9271 ext. 700 C: 480-272-2471
>> [email protected]<mailto:[email protected]>
>> www.mfpdesign.com<http://www.mfpdesign.com>
>>
>> Send large files to us via:
>> https://www.hightail.com/u/MFPDesign<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hightail.com%2Fu%2FMFPDesign&data=02%7C01%7C%7C1121d49f9e6b4cf248f108d4df580e77%7C14e5497c16da42e69ffa77d19bafe511%7C0%7C0%7C636379016677342180&sdata=eGdMZGu2wXhUupGwgGTrqF3b54OP5%2BAZvlHhABSexWY%3D&reserved=0>
>>
>> From: Sprinklerforum <[email protected]> On
>> Behalf Of Jerry Van Kolken via Sprinklerforum
>> Sent: Thursday, March 18, 2021 5:03 PM
>> To: [email protected]
>> Cc: Jerry Van Kolken <[email protected]>
>> Subject: Different Levels of protection open to each other in the same hazard
>>
>> I've had this review comment come up and want to know if there was any way
>> to argue it.
>>
>> I have a project where each level of the building has its own system. There
>> are areas where the lower level opens into the upper level. Because these 2
>> level are not complete separate the reviewer is asking me to protect them
>> with the same system.
>>
>> Jerry Van Kolken
>> Millennium Fire Protection Corp.
>> 2950 San Luis Rey Rd.
>> Oceanside, CA 92058
>> (760) 722-2722 FX 722-2730
>>
>> CONFIDENTIALITY NOTICE This e-mail and any attachments are for the sole use
>> of the intended recipients and contain information that may be confidential
>> or legally privileged. If you have received this e-mail in error, please
>> notify the sender by reply e-mail and delete the message. Any disclosure,
>> copying, distribution, or use of this communication by someone other than
>> the intended recipient is prohibited.
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]<mailto:[email protected]>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org<http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org