12.34 hours is a long time for the Capt. to stand and wait, then wait 2 more 
hours.
Working backwards, if I wanted to pump it up in an hour, I'd need a 400 gpm 
pump that made 200#.
I do have a friend and competitor 2 miles from here with 2 trailer mounted 
Patterson diesels he does bridge and tunnel standpipes with...
All I can do is ask.

Thanks Vince and Brad.

-----Original Message-----
From: Sprinklerforum <[email protected]> On Behalf 
Of Vince Sabolik via Sprinklerforum
Sent: Saturday, April 17, 2021 3:20 PM
To: [email protected]
Cc: Vince Sabolik <[email protected]>
Subject: How long to pump up a standpipe?

My friend Brad Casterline wanted to offer an answer  to Tom Duross' 
question about how
long it would take to pump up a standpipe.

Please note, I'm not this smart!

P1=75 psi/.433=173 ft.
P2=200 psi/.433=462 ft.
deltaP=289 ft.
V1=5000 gal/7.48=669 ft^3.
P1V1=115,737 ft/ft^3, /289 ft=400 ft^3.
4 gpm/7.48/60=.009 ft^3/s.
400 ft^3/.009 ft^3/s=~12 hours.
-- 


*Vince Sabolik*

*West Tech Fire Protection, Inc.***

11351 Pearl Road   /   Strongsville, Ohio   44136

Phone 440 238-4800    Fax 440 238-4876   Cell 440 724-7601