If you just cant get the FDC moved, maybe add a pressure regulating valve or relief valve to prevent system overpressure? Not the most-best way to go, but better than blowing the system apart?
Matt -----Original Message----- From: Sprinklerforum <[email protected]> On Behalf Of Mike Morey via Sprinklerforum Sent: Tuesday, April 20, 2021 2:11 PM To: [email protected] Cc: Mike Morey <[email protected]>; Brian Harris <[email protected]> Subject: RE: FDC & Pump Suction Is cap it and put one on the building an option? Generally that's what we'd do in that scenario as there isn't much else you can safely do because of the compound pressure increase potential with a fire pump. Presumably you have to put a test header somewhere, just add an FDC as well? Of course then hydrant distance comes in to play as well. Mike Morey CFPS 3229 * NICET S.E.T. 123677 Project Manager * Fire Protection Group Shambaugh & Son, LP an EMCOR Company 7614 Opportunity Drive * Fort Wayne, IN * 46825 direct 260.487.7824 / cell 260.417.0625 / fax 260.487.7991 email [email protected] -----Original Message----- From: Sprinklerforum <[email protected]> On Behalf Of Brian Harris via Sprinklerforum Sent: Tuesday, April 20, 2021 3:09 PM To: [email protected] Cc: Brian Harris <[email protected]> Subject: FDC & Pump Suction BE ADVISED - This email originated outside EMCOR. 8.17.2.4.8 (2016) States the FDC cannot be located on the suction side of a pump. If a pump is being added to an existing system and the current FDC is in the yard what is the best way to handle this? Brian Harris, CET BVS Systems Inc. Design Manager https://urldefense.com/v3/__http://bvssystemsinc.com__;!!FaxH778!Oa95dsu6TI9Hj7kAeXEmYhi-WKVOTMpEuNpYZClEf07ApkGuVdkxvIwISy803Y3I$ <https://urldefense.com/v3/__http://bvssystemsinc.com/__;!!FaxH778!Oa95dsu6TI9Hj7kAeXEmYhi-WKVOTMpEuNpYZClEf07ApkGuVdkxvIwIS5Dr4aGJ$ > Phone: 704.896.9989 Fax: 704.896.1935 _______________________________________________ Sprinklerforum mailing list [email protected] https://urldefense.com/v3/__http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org__;!!FaxH778!Oa95dsu6TI9Hj7kAeXEmYhi-WKVOTMpEuNpYZClEf07ApkGuVdkxvIwISwwwknZk$ This message is for the named person's use only. It may contain confidential, proprietary or legally privileged information. No confidentiality or privilege is waived or lost by any mistransmission. If you receive this message in error, please immediately delete it and all copies of it from your system, destroy any hard copies of it and notify the sender. You must not, directly or indirectly, use, disclose, distribute, print, or copy any part of this message if you are not the intended recipient. _______________________________________________ Sprinklerforum mailing list [email protected] https://linkprotect.cudasvc.com/url?a=http%3a%2f%2flists.firesprinkler.org%2flistinfo.cgi%2fsprinklerforum-firesprinkler.org&c=E,1,Lpx3tcRLpwiaxhRN_jgQvczpWoBVrpZ-_cMaxqSwti-hybygSBkkctPb9h9BqHqASuUDRZpIpde_X8ZfGbcUopm8WVscaRNi-wydT9N_rQ,,&typo=1 _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org