I'd sure be interested in hearing more on this subject.
"Listing" only partially answers the question.
Roll groove v. cut groove makes a difference.
If the bottom line is as cheap as possible then you go one route.
If the bottom line is an effective fire sprinkler system for the life  of the 
building, you go a different route.

Scott
 
Office: (763) 425-1001 x 2
Cell: (612) 759-5556

-----Original Message-----
From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Tom Noble via Sprinklerforum
Sent: Friday, April 30, 2021 8:14 AM
To: Ron Greenman via Sprinklerforum
Cc: Tom Noble
Subject: Re: Dry System Couplings

NFPA 13 2016 edition section 6.5.3.2 only requires the couplings to be listed 
for dry system use.  If the coupling is listed for use in dry or precaution 
systems it is fully acceptable to be used. Some manufactures will suggest to 
use a “Flush or Tri-seal” gaskets in cold storage or freezer applications to 
prevent the water build up in the gasket itself.  Ultimately, not a code 
requirement.  

The above is my opinion and has not been processed as a formal interpretation 
in accordance with the NFPA Regulations Governing Committee Projects. This is 
provided with the understanding that the AFSA assumes no liability for this 
opinion or actions taken on it and they are not to be considered the official 
position of the NFPA or its technical committees. AFSA cannot provide design or 
consulting engineering services, and this opinion should therefore not be 
considered, nor relied upon, as such.
 
> On Apr 30, 2021, at 7:42 AM, Taylor Schumacher via Sprinklerforum 
> <sprinklerforum@lists.firesprinkler.org> wrote:
> 
> I'm digging through coupling data sheets and I'm seeing that most are listed 
> for use in wet and dry systems even when they do not have the gap seal. Is 
> there a requirement for using gaskets that have this gap seal gasket or is it 
> more of a best practice thing?
> 